I have D1 jumpered to D2.  My motor is an LSMV100L 3hp.

The scaling is because the modbus registers are frequency x 10,
and I have a four pole motor.  So the setpoint in register 2 for
1000RPM would be 1000/60*2*10 = 1000 / 3.

P-01 = 7500.
P-02 = 0
P-03 = 5.0
P-04 = 5.0
P-05 = 2
P-06 = 0
P-07 = 230
P-08 = 10.9
P-09 = 50
P-10 = 1430
P-11 = 0.1
P-12 = 3
P-13 = 0
P-14 = 201
P-15 = 0
P-16 = U 0-10
P-17 = 8
P-18 = 1
P-19 = 100

P-31 = 1
P-36 = 1 115.2 0

My machine is a bit disconnected at the moment as I stripped down
the x and y axes for a thorough cleaning.  If you need me to check some
more things I can probably get it reconnected later today or tomorrow.

-- Ralph
________________________________________
From: Viesturs Lācis <[email protected]>
Sent: Monday, October 5, 2026 10:22 AM
To: Enhanced Machine Controller (EMC)
Subject: Re: [Emc-users] How to modbus?

CAUTION: This email originated from outside the Walla Walla University email 
system.


pirmd., 2026. g. 5. okt., plkst. 04:31 — lietotājs Ralph Stirling via
Emc-users (<[email protected]>) rakstīja:
>
> I have an Invertek Optidrive E3 as well, with usb-to-rs485 control.  I've 
> uploaded my files to:
>
> https://gab.wallawalla.edu/~ralph.stirling/projects/linuxcnc/rmc2/
>

I tried to replicate your setup, even renamed all the HAL_TX_NAME and
other parameters to match your setup just to make sure there is no
chance for error.
The result is that there are no errors in terminal when I start
LinuxCNC from there and mb2hal.vfd_rd.num-errors and other num_errors
pins remain at 0 which seems to me that transactions are working. That
is the good news.

So in HalShow I tried to set mb2hal.vfd_wr.speed.int or
mb2hal.vfd_wr.speed.float value between min and max speed and
mb2hal.vfd_ctrl.control.int value set to 1 and there comes the bad
news - nothing happens, it does not try to move the motor. I was
wondering if there is something missing in VFD settings or I need to
connect some of inputs?
I am using this manual:
https://fusionfluid.com/images/Documents/manuals-documentation/invertek_vfd/Invertek_Manual-v200.pdf
Motor parameters, in case they matter: P-01 = 24000; P-02 = 1800; P-03
= 6.0; P-04 = 7.0; P-05 = 0; P-06 = 0; P-07 = 400; P-08 = 16.0; P-09 =
200; P-10 = 12000; P-11 = 2.0
Parameters related to modbus: P-12 = 3; P-15 = 5; P-31 = 1; P-36 = 1 115.2 3000;
Am I missing something?
I have a switch to connect D1 to +24V, I tried with both switch open and closed.

And can you please explain why do you multiply/divide the speed
command and speed feedback by 3 in your modspindle.comp? To get the
scaling correct?

Viesturs


_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users


_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to