True.  I actually meant I've only seen 20A outlets in commercial installations. 
 My house is wired with 20A circuits and 15A outlets.

On October 20, 2015 10:36:44 PM MDT, EVDL Administrator via EV 
<ev@lists.evdl.org> wrote:
>On 20 Oct 2015 at 19:34, Mike Nickerson via EV wrote:
>
>>  I've seen 20A circuits, but only in commercial installations. 
>
>You'll see plenty of 20a branch circuits in homes - all newer homes are
>
>wired this way - but 20a receptacles on them are indeed pretty rare.  
>
>This is because the code has an exception allowing cheaper 15a-rated 
>receptacles on a 20a branch circuit, as long as there's more than one
>outlet 
>on the circuit.  If there's only one receptacle on the circuit, it must
>be a 
>20a-rated recept.  (Code experts argue over whether a duplex receptacle
>
>counts as one or two outlets.)
>
>IIRC, the code ALLOWS but doesn't REQUIRE 20a-rated receptacles on a 
>multiple-receptacle 20a branch circuit.  I installed 120v 20a recepts
>on the 
>branch circuit in my garage to allow for better EV charging, though I'm
>not 
>100% convinced that (once you're beyond the 50 cent bargain bin junk 
>receptacles) there's much difference between the guts of a 15a-rated
>recept 
>and those of a 20-a rated recept.
>
>One more note about this.  Because code limits sustained load on a
>branch 
>circuit to 80% of its maximum, you can charge at no more than 1920
>Watts 
>from a 120v 20a residential branch circuit.  If your EV gets 250 Wh/mi
>and 
>has a typical 80% charging efficiency, you gain just over 6 miles of
>range 
>per hour of charging.  If you sleep 8 hours and charge while you sleep,
>
>that's 48 miles you can drive per day.
>
>It could be more than that, since some switchmode chargers do better
>than 
>80% efficiency.  Also, staying below 80% SOC increases battery charging
>
>efficiency.  But that's a pretty good rule of thumb.
>
>You're much better off going with a 240v circuit and charger.  A 240v
>20a 
>circuit gives you 3840 Watts, for over 12 miles of range per hour of 
>charging - 96 miles overnight.
>
>A 50a range / welder circuit is an even better bet, as long as your
>charger 
>has the guts to use it.  That recept allows 9.6kW charging.  At that
>rate 
>the EV described above gains over 30 miles of range for each hour of 
>charging - about 245 miles overnight.
>
>David Roden - Akron, Ohio, USA
>EVDL Administrator
>
>= = = = = = = = = = = = = = = = = = = = = = = = = = = = =
>EVDL Information: http://www.evdl.org/help/
>= = = = = = = = = = = = = = = = = = = = = = = = = = = = = 
>Note: mail sent to "evpost" and "etpost" addresses will not 
>reach me.  To send a private message, please obtain my 
>email address from the webpage http://www.evdl.org/help/ .
>= = = = = = = = = = = = = = = = = = = = = = = = = = = = =
>
>
>_______________________________________________
>UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
>http://lists.evdl.org/listinfo.cgi/ev-evdl.org
>Read EVAngel's EV News at http://evdl.org/evln/
>Please discuss EV drag racing at NEDRA
>(http://groups.yahoo.com/group/NEDRA)