More than somewhat off topic, but what the heck.

First off, the "joules" rating of your UPS probably refers to its built in 
TVSS's ability to absorb surge energy.  

That strongly suggests that you have a small office or home device.  These 
usually cost in the low to mid 2-figures to the low 3-figures.  They're 
meant to keep your desktop computer and monitor going long enough to save 
your work and shut down in an orderly manner, not to keep on working.

The battery in these is tiny, usually good for no more than 50-80 watt-hours 
at full load.  There's no point to connecting bigger batteries to them 
because their inverters aren't suited to continuous use.  They will overheat 
and (if you're lucky) shut down.  Also it's worth noting that the waveform 
from these cheap inverters is usually pretty hideous.

A larger commercial UPS will typically be a cabinet a few feet square that 
sits on the floor.  I worked in a place dependent on electronics that used 
these as temporary sources until the building genset could start and 
stabilize, and the automatic transfer switch change over to the genset.

These larger UPSes are much more robust and can work continuously, but 
they're still limited by their battery capacity.  They also aren't cheap.  
They cost in the upper 3 figures to well into the thousands.  Sometimes you 
can find used ones cheaply on Ebay and fix them up, though.

I'm not an expert on this, but here's another thought for you.

I set up a standby power system here many years ago, to keep our 
refrigerator, freezer, and water pump working, and to provide power to a 
blower on our fireplace insert, in case of power cuts.

My original idea was to measure the loads, calculate the duty cycle for each 
load, and size a battery to run the loads for 24 hours.  I don't recall the 
result but I decided that it was more (in cost and size) than I wanted to 
get into, so I settled for eight group 24 gel batteries in series-parallel 
for 24 volts at around 3.6 kWh.

I bought a used boat anchor - I mean a Trace 24 volt 2.5kW inverter, which 
to my surprise turned out to be just barely able to start the water pump.  

I moved the circuits to be protected to a Square D transfer subpanel.  This 
is a nifty and relatively affordable gadget with 2 main breakers and  a 
handful of branch circuit breakers (mine has 4).  There's a clever 
mechanical rocker between the main breakers so that only one of them can be 
on at a time.  One main breaker is connected to the mains (actually to a 
subfeed from the main panel), and the other is tied to my inverter through a 
power inlet (male panel mount receptacle).

This setup served me well a few times, but over the years I've let the 
battery decline.  I doubt that I could get more than an hour or so out of it 
now.  But I don't really worry about it because I've realized that (1) we 
don't have as many power cuts as I expected; and (2) they usually only last 
a few hours.

Others may have better suggestions for you.  Good luck!

David Roden, EVDL moderator & general lackey

To reach me, don't reply to this message; I won't get it.  Use my 
offlist address here : http://evdl.org/help/index.html#supt

= = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = 
     Some people, when confronted with a computer programming 
     problem, think "I know, I'll use regular expressions." 
     Now they have two problems.

                                            -- Jamie Zawinski
= = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = 

_______________________________________________
Address messages to [email protected]
No other addresses in TO and CC fields
UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
ARCHIVE: http://www.evdl.org/archive/
LIST INFO: http://lists.evdl.org/listinfo.cgi/ev-evdl.org

Reply via email to