Yes.........but RV's can have a weird problem.    When operating in stand alone 
mode (i.e. self supported and not connected to the grid)  they often act like a 
house in that the inverter/generator makes its own 120|240 and therefore the 
ground and neutral are often bonded together (at one place...in the RV)...and 
connected to the frame.    This means neutral and ground are connected 
together.....at one place....probably the frame    So it's just like a house.

It makes sense in. stand-alone mode (i.e. NOT connected to external power) and 
works just like a house in that if RV internal GFI (in the RV) senses current 
going to "ground" (i.e. frame) it trips the internal GFI   or breaker 

  So if your RV dryer connects the neutral or hot to the RV dryer metal box 
which is "grounded" , then internal RV GFI trips. and you kept from being 
electrocuted.   The ground effectively acts like a neutral to provide a path to 
sink the current and blow a breaker (or GFI).    

Keep in mind that normal NON GFI  breakers also expect a big enough ground wire 
even though in theory no current should pass through ground....BUT if it 
does,then the ground wire must be big enough to handle enough current to blow 
the breaker...   If you use a 1 Mohm resistor for ground, then the breaker will
never get 20 amps and it'll never blow, but the case can still be 120v

The problem is when you connect the RV to external power because NOW the RV 
neutral-ground bonding creates a path to ground.   So if you power the RV via
an external GFI, some of the current may come back through the external ground 
because now you effectively have 2 paths back to the bonding point of the 
house.      It's as if you had a huge appliance where neutral and ground were 
connected together. Not good.

it's bad.   In fact I think most RV's will pop an external GFI.  (at least the 
ones I've seen).    Not good.

I suppose the right answer is to have something inside the RV that switches 
between bonding and not-bonding depending whether you are stand alone or
not stand alone.

A similar problem can happen if you try to give temporary emergency power to 
your neighbor via an extension cord.

I'm not condoning it, but unfortunately it's pretty common situation that most 
people seem blissfully unaware.


On Saturday, September 4, 2021, 3:03:13 PM PDT, EVDL Administrator via EV 
<ev@lists.evdl.org> wrote: 

> I thought you could mix ground with neutral?

Ground and neutral are bonded together at only one point in your house.  
Usually that's at the main panel or main disconnect.  From that point on, 
ground and neutral are kept totally separate.  

You can't use the equipment ground as a substitute for neutral.  It creates 
a potentially hazardous situation and will trip a GFI, including the one in 
an EVSE.  To charge at 120v, you'll need an appropriately sized transformer. 

David Roden, EVDL moderator & general lackey

To reach me, don't reply to this message; I won't get it.  Use my 
offlist address here : http://evdl.org/help/index.html#supt

= = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = 
    People don't sleep enough, and they all seem to be hunting 
    something that can't be caught.  You think you're the dominant 
    species just because you go to the bathroom in a bowl instead 
    of a box.  But who's cleaning up after whom? 

                      -- Souseme, "Felines of New York"

= = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = = 

_______________________________________________
Address messages to ev@lists.evdl.org
No other addresses in TO and CC fields
UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
ARCHIVE: http://www.evdl.org/archive/
LIST INFO: http://lists.evdl.org/listinfo.cgi/ev-evdl.org