<br><font size=2 face="sans-serif">Gaylon, I can only offer initial thoughts.</font>
<br><font size=2 face="sans-serif">How are you determining the drift over one year ? 
Is it that your MW output has changed relative to a controlled water temperature ? If 
this is the case are you sure the drift is caused by the temperature measurment end of 
your controlled system ? i.e. have you verified the drift against another measurment 
method ?</font>
<br>
<br><font size=2 face="sans-serif">How long are you measuring this temperature with 
the same RTD/FM combination ? You could be seeing drift due to RTD degradation/time, 
degradation of wiring connections, or some form of &quot;cooking&quot; within the FBM 
circuitry. Is there any change in the drift rate over the year which might suggest 
seasonal ambient temperature changes not being correctly compensated for ?.</font>
<br>
<br><font size=2 face="sans-serif">Good luck,</font>
<br><font size=2 face="sans-serif">Gabriel.</font></x-html>