Satish,

The OUTSEL block is set up to handle reset windup & block initialization
handling. It can be used where you have a normal PID loop that should be
bumplessly interupted when a second controlled variable reaches a constraint
target.  Let's say you were normally operating with a fixed and steady gas
flow to a vessel.  In case the vessel pressure was getting close to the
relief valve setting you decide that the normal feedrate must be cut.  You
set the SELOPT parameter to 2 for "Low" selection and add a second PID
Pressure control loop with a setpoint somewhat below the relief valve
setting. Properly configured: at the moment the pressure rises to the
setpoint of the pressure controller the flow control valve will just start
to close (from it's current position) and the loop will become a pressure
controller with a minimum flow constraint.  When the vapor removal rate from
the vessel is increased the pressure controller will open the flow control
valve until the flow setpoint is achieved and the flow controller will now
bumplessly resume control of the valve.  The SIGSEL block is possible but
the OUTSEL block was built for this specific application.  Many
implementations are possible. Hope this answered your question.

Rick Rys
R2Controls



-----------------------------------------------------------------------
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]

Reply via email to