[ 
https://issues.apache.org/jira/browse/PLC4X-202?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=17126066#comment-17126066
 ] 

Matthias Milan Strljic commented on PLC4X-202:
----------------------------------------------

[~itaross] you right i also see there the same issue. That is just because i 
tried to stick with the OPC naming string with --
{code:java}
"ns=2, [identifier]=[value]{code}

> OPC-UA Driver cannot write Unsigned Types
> -----------------------------------------
>
>                 Key: PLC4X-202
>                 URL: https://issues.apache.org/jira/browse/PLC4X-202
>             Project: Apache PLC4X
>          Issue Type: Bug
>          Components: Driver-OPC-UA
>    Affects Versions: 0.7.0
>            Reporter: Alessandro Rossignoli
>            Priority: Major
>
> Currently, unsigned types are not supported in writing direction from the 
> driver although they are fully supported by Eclipse Milo and in reading.
> Actually I have applied a modification and tested it to be able to support 
> these types. It is kind of the same patch applied for BigIntegers but done 
> introducing UShort and UInteger from Eclipse Milo.
> The downside is that every driver will use the Eclipse Milo types, being the 
> JVM missing unsigned types. I don't know if you have a better solution or if 
> using Milo types in all the drivers is acceptable for you.
> I am open for suggestions :)
>  
> (PS. when I will complete all the testing I will create 3 separate PR for 
> issue #200, #201 and this one)



--
This message was sent by Atlassian Jira
(v8.3.4#803005)

Reply via email to