https://issues.apache.org/jira/browse/PLC4X-202?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=17126075#comment-17126075
]
Matthias Milan Strljic commented on PLC4X-202:
----------------------------------------------
Another option would be a browse of the established connection to get a list of
all utypes which would be a potential problem for dynamic opc servers. I
struggle also a bit with the addition to the address string and try to find
another way to stick with the opc specification
> OPC-UA Driver cannot write Unsigned Types
> -----------------------------------------
>
> Key: PLC4X-202
> URL: https://issues.apache.org/jira/browse/PLC4X-202
> Project: Apache PLC4X
> Issue Type: Bug
> Components: Driver-OPC-UA
> Affects Versions: 0.7.0
> Reporter: Alessandro Rossignoli
> Priority: Major
>
> Currently, unsigned types are not supported in writing direction from the
> driver although they are fully supported by Eclipse Milo and in reading.
> Actually I have applied a modification and tested it to be able to support
> these types. It is kind of the same patch applied for BigIntegers but done
> introducing UShort and UInteger from Eclipse Milo.
> The downside is that every driver will use the Eclipse Milo types, being the
> JVM missing unsigned types. I don't know if you have a better solution or if
> using Milo types in all the drivers is acceptable for you.
> I am open for suggestions :)
>
> (PS. when I will complete all the testing I will create 3 separate PR for
> issue #200, #201 and this one)
--
This message was sent by Atlassian Jira