https://issues.apache.org/jira/browse/PLC4X-344?page=com.atlassian.jira.plugin.system.issuetabpanels:comment-tabpanel&focusedCommentId=17620235#comment-17620235
 ] 

Christofer Dutz commented on PLC4X-344:
---------------------------------------

In that case I would assume it's using poll() instead of remove() which is the 
fix and not all the other changes ... and yeah ... the stacktrace seems to 
imply that. Then I think we should only change those 3 lines (the poll and the 
if clause)

> spi.transaction.RequestTransactionManager is not thread safe
> ------------------------------------------------------------
>
>                 Key: PLC4X-344
>                 URL: https://issues.apache.org/jira/browse/PLC4X-344
>             Project: Apache PLC4X
>          Issue Type: Bug
>          Components: Driver-S7, PLC4J
>         Environment: Siemens IOT 2050, debian. PLC4J via kotlin
>            Reporter: Robin
>            Priority: Major
>         Attachments: PLC4X-344.patch, errorConnect.png
>
>
> When running a s7 connection to an PLC sometimes the connection halts and 
> this error is thrown in the log. It seems like the processWorklog function 
> uses a thread safe queue but is itself not threadsafe throwing this error.
>  
> We're using an single connection to the plc. Reading two datablocks. Each 
> datablock is read by a different handler running in a separate thread but 
> using the same instance of PLC4J.



--