Both of the modules you mentioned have built in cjc sensors. You
mentioned the 1303 terminal block then later called it a 1300.  The
1303 should have a more accurate cjc reference than the 1300. I have
not used the 1112 but since it is designed specifically for
Thermocouple measurements they should have a decent cjc sensor
network.  I will mention that the miniconnector plugs should be the
right type for the T type you are using but I imagine you have done
this.

In the scan mode your 1102 module will continue to scan the cjc so
changes in ambient temperature at the chassis should be compensated
for.  Since the 1112 are newer module they should do the same. Some of
the older isolated modules only picked up the cjc reference at on the
initialization of the scan.  I have used the 1102 modules with the
1303 terminal blocks for several years. The accuracy of this
combination usually keeps me within a couple deg F. when I check the
system.

If you are using the 1303 terminal block make sure you have the right
resistor network for your application. Check your documentation for if
you have the 10 ohm bias resistor in and your tc is grounded you will
see a significant error.

There are ways of using an external CJC to improve your accuracy if
needed. These methods will increase the cost of your system, as they
will require additional hardware.