Thank you sir for answering my question.

--- On Mon, 10/6/08, Ray Zimmerman <[email protected]> wrote:

> From: Ray Zimmerman <[email protected]>
> Subject: Re: loss equation
> To: "MATPOWER discussion forum" <[email protected]>
> Date: Monday, October 6, 2008, 12:14 PM
> If you are referring to the quantity that is printed as the
> "Losses  
> (I^2 * Z)" in the output, for each branch it is
> computed as,
> 
>    loss =  (Vf / tap - Vt) ^ 2 / (R + j X)
> 
> where Vf and Vt are the complex voltages at the
> "from" and "to" ends  
> of the branch, R and X are the series resistance and
> reactance of the  
> branch, and tap is the tap ratio for a transformer (1
> otherwise). This  
> should give the losses in the series portion of the
> pi-model for the  
> branch. It does not include the shunt portions used to
> model line  
> charging.
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> 428-B Phillips Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> On Oct 6, 2008, at 6:44 AM, jigna pandya wrote:
> 
> > hello everybody,
> > i want to know that which method has been used to find
> active power  
> > loss and reactive power loss in N-R power flow method
> in matpower?
> >
> > thanks in advance
> >
> >
> >
> >


      