On 07/13/2010 12:52 PM, indra g.c. wrote:
In MATPOWER, the power flow result for the contingency cases show that
the generator sources violate their maximum reactive power limit but
maintain their specified voltage magnitude.
Whether it is possible or not to maintain the max. Reactive power limit?
Theoretically, if a generator source in a PV buses crosses the
reactive power limit, then we treat that bus as load bus. It is true
or not ? If it is true, why the power flow result for the contingency
cases show generator sources violate their maximum reactive power limit?
hello,
You need to enable the option to check Q-limits.
Have a look at 'help mpoption'
This should do the trick:
opt=mpoption;
opt(6)=1;
runpf(structure,opt)
Dirk
--
Dirk Van Hertem
Royal Institute of Technology, Stockholm
(and K.U. Leuven, ESAT-ELECTA)
tel (GSM): +32-498-61.74.98