That should be ...

mpopt = mpoption('ENFORCE_Q_LIMS', 1);


--
Ray Zimmerman
Senior Research Associate
211 Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645



On Jul 13, 2010, at 8:01 AM, amir khorsandi wrote:

hi
If you want that in power flow calculations, reactive power limits of 
generators satisfied use this commands:

mpopt = mpoption('ENFORCE_Q_LIMS', 0);
[baseMVA, bus, gen, branch, success, et] = runpf('case30',mpopt);

good luck



From: indra g.c. <[email protected]<mailto:[email protected]>>
To: [email protected]
Sent: Tue, 13 July, 2010 15:22:57
Subject: Help

In MATPOWER, the power flow result for the contingency cases show that the 
generator sources violate their maximum reactive power limit but maintain their 
specified voltage magnitude.
Whether it is possible or not to maintain the max. Reactive power limit?
Theoretically, if a generator source in a PV buses crosses the reactive power 
limit, then we treat that bus as load bus. It is true or not ? If it is true, 
why the power flow result for the contingency cases show generator sources 
violate their maximum reactive power limit?