Simon, Thanks for the input.
Yes, Pmax for the generator at bus 1 is 35 MW, which is 15 MW short of being able to supply the load alone, but (leaving both online) in this substation emulation it is desirable to fully use its capacity as its connection to the load has the lowest impedance. I'm thinking that, even though they are being modeled as substation busbars, the generators' operating points might be limited by their capability curves, is that correct? Regards, Guilherme Lira On Mon, Mar 21, 2011 at 6:36 AM, Simon Schneider <[email protected]> wrote: > Hi Guilherme, > > if you turn off the second gen (mpc.gen(2,8) = -1) you see, that several > other constraints are violated and the opf doesn´t converge. > The Generator at 1 isn´t powerfull enough to satisfy the load alone. > > Greetings > Simon > Am 3/20/2011 10:33 PM, schrieb Guilherme Lira: >> >> Ray/others, >> >> In order to test the power loss minimization, I have tried modeling >> the generators with equal linear costs simulating substation busbars. >> >> Please have a look at the attached m-file, it contains a simple test >> case consisting of two generators connected to a load, with different >> branch impedance values. Theoretically, minimizing losses would mean >> that the generator (substation busbar) connected to the load through >> the branch of lowest impedance would be serving the load at full power >> (Pmax), right? Can you please explain why it is not? >> >> Thanks, >> Guilherme > >