Ray/Simon,

Thank you for the information. Setting generator costs to the values
suggested by Prof. Ray did yield the expected results.

Best regards,
Guilherme Lira

On Tue, Mar 22, 2011 at 6:02 AM, Simon Schneider <[email protected]> wrote:
> Hey,
>
> I惴 not sure if it愀 possible for an OPF to do so, because I think the nearer
> you get a value to its constraint, the more it becomes "penalized".
> It gets weighted with a factor mu (see mpc.gen(n , 22:25 )?), so the
> objective function does not obtain the best solution with the power of one
> generator near its maximum.
>
> Also you have to consider the other constraints, like nodal voltage. The
> calculation trys to minimize the objective funtion and find the ideal
> balance between all constraints.
> At least that愀 what I think it does. I惴 not into the opf mechanisms very
> deep yet.
>
> Greetings
> Am 3/21/2011 1:13 PM, schrieb Guilherme Lira:
>>
>> Simon,
>>
>> Thanks for the input.
>>
>> Yes, Pmax for the generator at bus 1 is 35 MW, which is 15 MW short of
>> being able to supply the load alone, but (leaving both online) in this
>> substation emulation it is desirable to fully use its capacity as its
>> connection to the load has the lowest impedance. I'm thinking that,
>> even though they are being modeled as substation busbars, the
>> generators' operating points might be limited by their capability
>> curves, is that correct?
>>
>> Regards,
>> Guilherme Lira
>>
>> On Mon, Mar 21, 2011 at 6:36 AM, Simon Schneider<[email protected]>
>>  wrote:
>>>
>>> Hi Guilherme,
>>>
>>> if you turn off the second gen (mpc.gen(2,8) = -1) you see, that several
>>> other constraints are violated and the opf doesn愒 converge.
>>> The Generator at 1 isn愒 powerfull enough to satisfy the load alone.
>>>
>>> Greetings
>>> Simon
>>> Am 3/20/2011 10:33 PM, schrieb Guilherme Lira:
>>>>
>>>> Ray/others,
>>>>
>>>> In order to test the power loss minimization, I have tried modeling
>>>> the generators with equal linear costs simulating substation busbars.
>>>>
>>>> Please have a look at the attached m-file, it contains a simple test
>>>> case consisting of two generators connected to a load, with different
>>>> branch impedance values. Theoretically, minimizing losses would mean
>>>> that the generator (substation busbar) connected to the load through
>>>> the branch of lowest impedance would be serving the load at full power
>>>> (Pmax), right? Can you please explain why it is not?
>>>>