I am assuming you are running this with offers/bids defined by what is in 
gencost. In the first case, the incremental cost of generation between 50 MW 
and 100 MW of output is $15/MWh. Likewise the incremental benefit for the load 
between 60 MW and 90 MW is also $15/MWh. For the (lossless) DC OPF problem, 
this means that the objective function value does not change as the dispatch 
changes between 60 and 90 MW ... i.e. for the exact bids and offers you are 
using there is no unique minimizing solution to the DC problem. For the AC 
problem, the losses create a small price difference between the buses, 
eliminating solutions with greater than 60 MW of demand, so there is a unique 
solution.

In the case with the line constraint at 50 MW, once again, you are creating an 
anomaly by setting the constraint value to fall *exactly* on the corner point 
of the generator's cost function. If you set it to something slightly less than 
50, then the prices will be pretty close to the expected $10 and $18. If you 
set it slightly greater than 50, then the prices will be $15 and $18. Strictly 
speaking, the node 1 price for a line capacity of exactly 50 MW is not uniquely 
defined. It can be anything between $10 and $15.

Hope this helps,

-- 
Ray Zimmerman
Senior Research Associate
211 Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645



On May 12, 2011, at 12:58 PM, Santiago Chamba wrote:

> Dear Professor Zimmerman,
>  
> I think that there is a probable mistake in the auction method (smartmarket), 
> specifically in DC OPF. I run a smartmarket and OPF (DC and AC) without fixed 
> load, i.e., the two nodes system only has  generators offers and demand bids 
> (inelastic).
>  
> When, I run AC OPF the results are correct, but with DC OPF the results may 
> be wrong, because the inyections and extractions electricity are very 
> different to the AC responses:
>  
> Node              DC OPF                            DC OPF
>                 Pot          Lambda                Pot          Lambda
>                 MW           $/MW                   MW         $/MW
> 1           70.8298      15                   60.0394     15.00
> 2         -70.8298       15                  -60.0067     15.016
>  
> I think the correct responses for DC OPF is 60 MW in the two nodes. Why are 
> the AC and DC results so different?
>  
> When, the capacity line decreases to 50 MW, the inyections and extractions 
> electricity are correct, but the prices changes:
>  
> Node              DC OPF                            DC OPF
>                 Pot          Lambda                Pot          Lambda
>                 MW           $/MW                   MW         $/MW
> 1                50        11.32                   49.99        10
> 2               -50        18.00                  -49.97       18
>  
> I think the correct responses for DC OPF is 10 and 18 ($/MW). Why are the 
> prices (AC and DC) in the node 1 so different?
>  
> Please, explain me What is my mistake? or Where can I modify the mistake?. 
> Because I need the model for my investigation. 
>  
> Thank
>  
>  
>  