Dear Dr Ray,
Thanks for the explanations.
Kind regards

Idris
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ray Zimmerman
Sent: 10 January 2012 14:40
To: MATPOWER discussion forum
Subject: Re: AC power flow for multiple generators

MATPOWER's power flow does not currently handle distributed slack, so the only 
time it makes sense to specify more than one slack bus is in an islanded 
system, where you need one in each island. If you set multiple reference buses 
in a fully connected network, it will distribute the slack among the two buses 
as required to make the voltage angles at both buses equal to the specified 
angles (probably not what you want). Also, as you have seen, currently if there 
are multiple generators at a reference bus, all of the slack is assigned to the 
first generator.

--
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645





On Jan 10, 2012, at 7:14 AM, Idris Musa wrote:


Dear all,
I want run AC power flow, considering multiple generators with possibility of 
Islanding using MATPOWER 4.1.
In addition to the grid supply I have five generators of equal output capacity 
at particular bus location. I defined this bus location as slack bus. This 
means I have two slack buses (including the grid supply). When I run MATPOWER 
AC power flow, with the grid connected, one of the generators (the first 
generator of the five connected) is taking care of system losses, showing that 
the chosen generator has unlimited capacity and is also absorbing negative 
active power. I am assuming a distributed generator (which could be synchronous 
generator, fuel cell etc) is this physically feasible? I had expected the grid 
supply been the first slack bus to take care of the system losses and provide 
other support for the network.  I would be glad if someone could advice on how 
to go about it.

Idris Musa