Dear shiyang,
Thanks for your contributions. In fact I had thought in the direction of your 
first option.
During the grid connection I allow the grid supply to be the only slack bus. 
The five generators bus location defined as PV bus. Then in Islanding I 
re-define the bus as the slack bus since the grid connection is now lost. I 
will have a look at other options you suggested. 
Once more many thanks.
Idris 


>-----Original Message-----
>From: [email protected] [mailto:bounce-39129280-
>[email protected]] On Behalf Of ???
>Sent: 10 January 2012 14:46
>To: 'MATPOWER discussion forum'
>Subject: Re: AC power flow for multiple generators
>
>Dear Idris Musa,
>As far as I know version 4.1 explicitly allows more than one slack bus
>(bus it still cannot deal the situation when the Q output of any slack
>bus reach its limit). 'pfsoln.m' defined how to distribute the
>generations. From it we know Matpower assigned all active network loss
>undertaken by each slack bus to its first generator (version 4.1 make
>this available for all slack buses).
>I agree with you that the situation you mentioned is not physically
>meaningful. Thus, as my opinion:
>Firstly, with the grid connected you can define the PCC bus only as the
>slack bus, while without the connection, define the generator bus in
>this island as slack bus (the reason to define only one slack bus is
>that the electrical connection between PCC and the other slack bus is
>usually not weak enough, so setting their voltage angles both as given
>conditions is usually not reasonable -- how do you know the proper
>angles difference between the two slack buses? Absorbing P may be a sign
>that the setting angle of the slack bus is too small.); Secondly, if the
>P loss is large and you don't think assigning it to the first generator
>is sound, you can change the code of 'pfsoln.m', distribute P loss
>equally to each generator on the slack bus; Thirdly, the premise of that
>your slack bus P generation is reasonable, is that all other generators'
>P settings are proper. Negative P generation may imply others' P
>settings don't fit the real sistuation. Especially when you consider the
>island re-connect to the grid, I think decreasing the P generations in
>the island is quite normal.
>
>Shiyang, Li
>
>-----邮件原件-----
>发件人: [email protected]
>[mailto:[email protected]] 代表 Idris Musa
>发送时间: 2012年1月10日 20:15
>收件人: 'MATPOWER discussion forum'
>主题: AC power flow for multiple generators
>
>Dear all,
>I want run AC power flow, considering multiple generators with
>possibility of Islanding using MATPOWER 4.1.
>In addition to the grid supply I have five generators of equal output
>capacity at particular bus location. I defined this bus location as
>slack bus. This means I have two slack buses (including the grid supply).
>When I run MATPOWER AC power flow, with the grid connected, one of the
>generators (the first generator of the five connected) is taking care of
>system losses, showing that the chosen generator has unlimited capacity
>and is also absorbing negative active power. I am assuming a distributed
>generator (which could be synchronous generator, fuel cell etc) is this
>physically feasible? I had expected the grid supply been the first slack
>bus to take care of the system losses and provide other support for the
>network.  I would be glad if someone could advice on how to go about it.
>
>Idris Musa
>
>
>
>
>
>