When running a simple power flow, the slack bus must provide *all* of the power 
needed make up the difference between the load+losses and the sum of the other 
generators. It cannot be restricted without changing the other generator 
dispatches, but then it isn't a simple power flow problem anymore, but rather 
some sort of re-dispatch problem (of which an OPF is one kind).

So in MATPOWER the PMAX column of the gen table is only used for OPF problems.

-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Feb 16, 2012, at 4:35 PM, iman wrote:

> Dear all,
> 
> 
> 
> Supposedly DNO doesn’t allow us to import more than 30 MW from the network 
> (and if we do we would be charged), is there any way to limit the power 
> coming from the slack up to 30 MW ?
> 
> I can see that there is a maximum real power output (MW) designated  in 
> column 9 of  Generator Data (mpc.gen); however when I increase the load by 
> running pf I can see P Generation from bus 1 is 127 MW ,no matter what the 
> value of “maximum real power output” is.
> 
> How can I solve this problem?
> 
> 
> -- 
> Best regards
> Iman
> 