Assuming that you want to specify a reactive dispatch capability
within the .9  power factor cone that we talked about earlier, and
assuming Pmin = 0 and Pmax = 1MW, then at Pmax the reactive dispatch
could be in [-0.4843, 0.4843] MVAr.  Then, the following parameters
define that cone for Matpower:

Pmin = 0
Pmax = 0
Qmax = 0.4843
Qmin = -0.4843
Pc1 = 0
Qc1min = 0
Qc1max = 0
Pc2 = 1
Qc2min = -0.4843
Qc2max = 0.4843




On Thu, Aug 30, 2012 at 4:56 PM, Richard Ngonga <[email protected]> wrote:
>
> Hi Carlos,
>
> Do I have to model photovoltaic generators in matpower like diesel
> generators? My aim is to model photovoltaic inverters as dispatchable
> reactive power sources using Matpower's trapezidal modeling of the (P,Q)
> feasible region. What is the best way to model them in matpower?
>
> Regards
>
> Richard
>
>> Date: Mon, 20 Aug 2012 12:23:10 -0400
>> From: [email protected]
>> To: [email protected]
>> Subject: Re: PV Generators and Transformer modelling
>>
>> So, if the reactive dispatch of your generators is constrained to be
>> within a 0.95 power factor, then you can use MATPOWER's trapezoidal
>> modeling of the (P,Q) feasible region. as opposed to simple bound
>> constraints on P and Q
>> for a generator. In your case, if Pmin reaches down to 0, then you have
>> more of a cone instead of a trapezoid.
>> This is best explained using a picture; see manual for details.
>>
>> carlos.
>>
>> Richard Ngonga wrote:
>> > Thanks for that, I mean photo voltaic. I am modelling PV generators
>> > that are able to dispatch reactive power(i.e operating at -0.95 to
>> > 0.95 power factor).
>> >
>> >
>> > > Date: Mon, 20 Aug 2012 01:34:09 -0400
>> > > From: [email protected]
>> > > To: [email protected]
>> > > Subject: Re: PV Generators and Transformer modelling
>> > >
>> > > Um, an unfortunate crisscross with acronyms... by PV generators do you
>> > > mean power-voltage as in classical power flow problem parlance or do
>> > you
>> > > rather mean "photo voltaic"?
>> > >
>> > > Richard Ngonga wrote:
>> > > >
>> > > > Hi there,
>> > > >
>> > > > I am working on a thesis on reactive power control on a distributed
>> > > > network with transformers and PV generators. Can I model the PVs as
>> > > > generators on a PV bus or should I model them as capacitors on a PQ
>> > > > bus? I'm also having problems modelling transformers from a 20KV
>> > > > network to a 0.4KV network; when I use the transformer ration 50 I
>> > get
>> > > > very large power flows and losses. The transformer data is: Sn
>> > 400KVA,
>> > > > Usc=10%, Uprm/Usec=20/0.4(KV) and Usec set=1.05.
>> > > >
>> > > > Regards
>> > >
>> > >
>>
>>

Reply via email to