Richard:

One easy way to minimize losses using the opf solver is to assign to all generators the same linear "fuel" cost. If all sources have the same cost, then the optimizer will try to minimize losses. However, you have to provide sensible VMIN, VMAX limits for all buses in the bus table, or the optimizer will simply try to raise voltages as much as possible.

Richard Ngonga wrote:
Carlos,

Thank you once more for your help. My objective is to solve an optimum power flow and I want to obtain an optimal voltage profile and minimise dissipation losses. I have modelled the Photovoltaic generators to inject active(Pmax=0.032MV) & reactive power and tested the network for convergency using pf before proceeding to the opf model. The network converged when I modelled the buses containing the photovoltaic generators as either slack bus or PQ bus but does not converge when I model the buses as PV. Would the situation change if I test the model using opf? I have one traditional generator modelled as a HV infinite source.

> Date: Sat, 1 Sep 2012 22:32:51 -0400
> From: [email protected]
> To: [email protected]
> Subject: Re: Photovoltaic Generators modelling
>
> Richard:
>
> Are you sure that you want to specify the power injections of the
> photovoltaic generators as zero in a power flow?
>
> The trapezoidal model for (P,Q) feasibility is intended for use in an
> optimal power flow setting, not a power flow setting. If you have all
> generators with Pg = 0 then you may not have enough generation to meet
> the demand. Do you have additional, traditional generators?
>
> In a power flow, the reactive dispatches are found such that the voltage
> at the bus is at the specified Vg. In an optimal power flow, the
> reactive dispatches are modulated to obtain an optimal voltage profile.
>
> Which is it that you want to achieve? Do you want to solve a power flow
> or an optimal power flow?
>
> Richard Ngonga wrote:
> > Hi ,
> >
> > I have modelled 20 photovoltaic generators in a 100 bus radial
> > distribution network with the parameters shown below(in the generator
> > field). The problem I am having is that when I model the nodes with
> > the Photovoltaic generators as PV buses the AC Newton Raphson loadflow
> > does not coverge, but when I model the same nodes as swing
> > buses(option 3) the network converges. My aim is to model
> > the photovoltaic generators as var controllers, is there a way this
> > can be done in Matpower?
> >
> > Pg=0
> > Qg=0
> > Pmin = 0
> > Pmax = 0
> > Qmax = 0.01563
> > Qmin = -0.01563
> > mBase=100
> > Pc1 = 0
> > Qc1min = 0
> > Qc1max = 0
> > Pc2 = 0.032
> > Qc2min = -0.01563
> > Qc2max = 0.01563
> >
> > Richard Ngonga
> >
> >
> > > Date: Thu, 30 Aug 2012 21:36:52 -0400
> > > Subject: Re: Photovoltaic Generators modelling
> > > From: [email protected]
> > > To: [email protected]
> > >
> > > Assuming that you want to specify a reactive dispatch capability
> > > within the .9 power factor cone that we talked about earlier, and
> > > assuming Pmin = 0 and Pmax = 1MW, then at Pmax the reactive dispatch
> > > could be in [-0.4843, 0.4843] MVAr. Then, the following parameters
> > > define that cone for Matpower:
> > >
> > > Pmin = 0
> > > Pmax = 0
> > > Qmax = 0.4843
> > > Qmin = -0.4843
> > > Pc1 = 0
> > > Qc1min = 0
> > > Qc1max = 0
> > > Pc2 = 1
> > > Qc2min = -0.4843
> > > Qc2max = 0.4843
> > >
> > >
> > >
> > >
> > > On Thu, Aug 30, 2012 at 4:56 PM, Richard Ngonga
> > <[email protected]> wrote:
> > > >
> > > > Hi Carlos,
> > > >
> > > > Do I have to model photovoltaic generators in matpower like diesel
> > > > generators? My aim is to model photovoltaic inverters as dispatchable > > > > reactive power sources using Matpower's trapezidal modeling of the
> > (P,Q)
> > > > feasible region. What is the best way to model them in matpower?
> > > >
> > > > Regards
> > > >
> > > > Richard
> > > >
> > > >> Date: Mon, 20 Aug 2012 12:23:10 -0400
> > > >> From: [email protected]
> > > >> To: [email protected]
> > > >> Subject: Re: PV Generators and Transformer modelling
> > > >>
> > > >> So, if the reactive dispatch of your generators is constrained to be > > > >> within a 0.95 power factor, then you can use MATPOWER's trapezoidal
> > > >> modeling of the (P,Q) feasible region. as opposed to simple bound
> > > >> constraints on P and Q
> > > >> for a generator. In your case, if Pmin reaches down to 0, then
> > you have
> > > >> more of a cone instead of a trapezoid.
> > > >> This is best explained using a picture; see manual for details.
> > > >>
> > > >> carlos.
> > > >>
> > > >> Richard Ngonga wrote:
> > > >> > Thanks for that, I mean photo voltaic. I am modelling PV generators > > > >> > that are able to dispatch reactive power(i.e operating at -0.95 to
> > > >> > 0.95 power factor).
> > > >> >
> > > >> >
> > > >> > > Date: Mon, 20 Aug 2012 01:34:09 -0400
> > > >> > > From: [email protected]
> > > >> > > To: [email protected]
> > > >> > > Subject: Re: PV Generators and Transformer modelling
> > > >> > >
> > > >> > > Um, an unfortunate crisscross with acronyms... by PV
> > generators do you
> > > >> > > mean power-voltage as in classical power flow problem
> > parlance or do
> > > >> > you
> > > >> > > rather mean "photo voltaic"?
> > > >> > >
> > > >> > > Richard Ngonga wrote:
> > > >> > > >
> > > >> > > > Hi there,
> > > >> > > >
> > > >> > > > I am working on a thesis on reactive power control on a
> > distributed
> > > >> > > > network with transformers and PV generators. Can I model
> > the PVs as
> > > >> > > > generators on a PV bus or should I model them as capacitors
> > on a PQ
> > > >> > > > bus? I'm also having problems modelling transformers from a
> > 20KV
> > > >> > > > network to a 0.4KV network; when I use the transformer
> > ration 50 I
> > > >> > get
> > > >> > > > very large power flows and losses. The transformer data is: Sn
> > > >> > 400KVA,
> > > >> > > > Usc=10%, Uprm/Usec=20/0.4(KV) and Usec set=1.05.
> > > >> > > >