That is not the Implicit Zbus Gauss method described in my dissertation. That 
is the standard Gauss-Seidel method that is already implemented in MATPOWER. 
And by the way, the easy way to run that one is …

opt = mpoption('PF_ALG', 4);
runpf(case_name, opt);

-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Oct 10, 2012, at 3:26 AM, Zeinab Ghofrani <[email protected]> wrote:

> Dear Dr Zimmerman
>  
> I implemented the Gauss method using the following codes, but still there is 
> convergence problem:
>  
>  
> case_name='case_dist_32bus';
> mpc = loadcase(case_name);
>  
> ref=[33]; pv=[];
> pq=1:32; pq=pq';
> V0=ones(size(mpc.bus,1),1);
> Sbus=makeSbus(mpc.baseMVA, mpc.bus, mpc.gen);
> Ybus=makeYbus(mpc);
> results=gausspf(Ybus, Sbus, V0, ref, pv, pq);
>  
> The system matpower data is attached to this email.
>  
> Thanks
> Zeinab Ghofrani
>  
> From: Ray Zimmerman <[email protected]>
> To: MATPOWER discussion forum <[email protected]> 
> Sent: Monday, October 8, 2012 7:49 AM
> Subject: Re: convergence of 32-bus distribution network PF
> 
> I wish I could. Unfortunately, the code I used for my thesis was tightly tied 
> to some proprietary data formats and it also does not run on current versions 
> of Matlab. I you already have the data in MATPOWER format, it would probably 
> be rather straightforward to implement the Implicit Zbus Gauss method, since 
> MATPOWER can easily build the Ybus matrix for you. That's probably the 
> approach I would take if I were you.
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> 
> On Oct 6, 2012, at 1:27 AM, Zeinab Ghofrani <[email protected]> wrote:
> 
>> Dear Dr Zimmerman;
>>  
>> Thanks for sending me your thesis, which was very useful. Could you please 
>> provide me with a reliable MATLAB code for running backward-forward sweep 
>> load flow on a radial distribution matpower case?
>>  
>>  
>>  
>>  
>> Zeinab Ghofrani
>> 
>> From: Ray Zimmerman <[email protected]>
>> To: MATPOWER discussion forum <[email protected]> 
>> Sent: Friday, October 5, 2012 6:21 AM
>> Subject: Re: convergence of 32-bus distribution network PF
>> 
>> My guess is that it may require a different power flow formulation, namely 
>> one that is specifically designed for radial distribution systems. Feel free 
>> to look at my dissertation and the references in it for some ideas.
>> 
>> -- 
>> Ray Zimmerman
>> Senior Research Associate
>> 419A Warren Hall, Cornell University, Ithaca, NY 14853
>> phone: (607) 255-9645
>> 
>> 
>> 
>> On Oct 5, 2012, at 2:37 AM, Zeinab Ghofrani <[email protected]> wrote:
>> 
>>> Dear all;
>>>  
>>> I'm tryning to run power flow on the 32 bus distribution system described 
>>> in the following paper:
>>> M. E. Baran and F. F. Wu, “Network Reconfiguration in Distribution Systems 
>>> for Loss Reduction and Load Balancing”, IEEE Trans on Power Delivery, 1989, 
>>> Vol 4(2), pp
>>> 1401-1407.
>>> I have chnaged the place of the tie switches so that the modified system 
>>> has a long latteral with high voltage drop. The power flow doesn't 
>>> converge, unless we set Vg of mpc.gen matrix to 1.3. How can I have a 
>>> converged load flow when Vg is set to 1?
>>> The data I use is attached to this email. Waiting for your reply.
>>> 
>>> Zeinab Ghofrani
>>> <case_dist_32bus.m>
>> 
>> 
>> 
> 
> 
> 
> <case_dist_32bus.m>

Reply via email to