Dear Dr Zimmerman,

GeneratorA has a fuel cost of $10/MWh. GeneratorB  has a fuel cost of  $12/MWh. 
GeneratorC has a fuel cost of $14/MWh.

a) I want to run the OPF, and I created this table. Is it correct?  


mpc.gencost = [ 

           %n   %c(n-1)    %co

2  0  0  2     10         0 ;

2  0  0  2     12         0 ;
2  0  0  2     14         0 ;
];

b) How does the program select how much Q each generator will generate, given 
that no fuel_cost for Q has been given ?
In other words, for the Generation of P , we added fuel cost in  $/MWh.  But 
for the generation of Q, we did not add such 

fuel cost. 

c) RATE_A is the MVA rating for a certain branch. To translate it into MW 
rating and MVAr rating we do the following:

MW = MVA * PF_load  and  MVAr = MVA* PF_load ?    (power factor of the load)    
 Correct?





________________________________
 From: Ray Zimmerman <[email protected]>
To: MATPOWER discussion forum <[email protected]> 
Sent: Friday, April 19, 2013 2:32 PM
Subject: Re: line loss
 


Since the branch parameters are expressed in p.u. they must be modified along 
with baseKV in order for them to represent the same physical parameters. As it 
turns out, when the impedance parameters and voltages are expressed in p.u. (as 
they are in MATPOWER), there is no effect whatsoever of changing baseKV of a 
bus. It is in fact, not needed at all for the power flow calculations. It's 
only relevance is as relates to converting p.u. impedances and voltages back to 
physical parameters.

-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Apr 18, 2013, at 3:27 PM, Hedayat Saboori <[email protected]> wrote:

Dear all
>I'm about to evaluate the effect of line nominal voltage on line
losses. I simply increase line connected bus voltages, run power flow, and
calculate losses. But, in spite of increasing voltage loss is constant in all
cases. I have developed a simple code for a 2 bus network. M-files are
attached. What is the problem? does nominal voltage change any 
thing?<case2.m><lineloss.m>

Reply via email to