a) Yes.
b) It chooses Q so as to minimize the cost of P.
c) For a branch, in general the power factor is not known ahead of time, so 
there is no direct correspondence between an MVA limit (which approximates a 
current limit) and MW or MVAr limit. (Also, this is not a MATPOWER question … 
I'm starting to feel like I'm doing your HW for you).

-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Apr 20, 2013, at 6:38 AM, Aftognosia Aftognosia <[email protected]> wrote:

> Dear Dr Zimmerman,
> 
> GeneratorA has a fuel cost of $10/MWh. GeneratorB  has a fuel cost of  
> $12/MWh. GeneratorC has a fuel cost of $14/MWh.
> 
> a) I want to run the OPF, and I created this table. Is it correct?  
> 
> mpc.gencost = [ 
>            %n   %c(n-1)    %co
> 2  0  0  2     10         0 ;
> 2  0  0  2     12         0 ;
> 2  0  0  2     14         0 ;
> ];
> 
> b) How does the program select how much Q each generator will generate, given 
> that no fuel_cost for Q has been given ?
> In other words, for the Generation of P , we added fuel cost in  $/MWh.  But 
> for the generation of Q, we did not add such 
> fuel cost. 
> 
> c) RATE_A is the MVA rating for a certain branch. To translate it into MW 
> rating and MVAr rating we do the following:
> MW = MVA * PF_load  and  MVAr = MVA* PF_load ?    (power factor of the load)  
>    Correct?
> 
> 
> 
> From: Ray Zimmerman <[email protected]>
> To: MATPOWER discussion forum <[email protected]> 
> Sent: Friday, April 19, 2013 2:32 PM
> Subject: Re: line loss
> 
> Since the branch parameters are expressed in p.u. they must be modified along 
> with baseKV in order for them to represent the same physical parameters. As 
> it turns out, when the impedance parameters and voltages are expressed in 
> p.u. (as they are in MATPOWER), there is no effect whatsoever of changing 
> baseKV of a bus. It is in fact, not needed at all for the power flow 
> calculations. It's only relevance is as relates to converting p.u. impedances 
> and voltages back to physical parameters.
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> 
> On Apr 18, 2013, at 3:27 PM, Hedayat Saboori <[email protected]> wrote:
> 
>> Dear all
>> I'm about to evaluate the effect of line nominal voltage on line losses. I 
>> simply increase line connected bus voltages, run power flow, and calculate 
>> losses. But, in spite of increasing voltage loss is constant in all cases. I 
>> have developed a simple code for a 2 bus network. M-files are attached. What 
>> is the problem? does nominal voltage change any thing?
>> <case2.m><lineloss.m>
> 
> 
> 