?Hi Shri,

>You can model it as a generator in MatPower with a negative Pmin, Pmax and a 
>positive Qmin, Qmax.


My thought was that if I do this Matpower won't recognize it as a dispatchable 
load and hence won't maintain a constant power factor - perhaps I'm mistaken 
here, I'll gave it a go though and it seems to be working.


>What kind of load is this????


Honestly, I don't know. See the load at bus 9 in the attached model. It is one 
of the test cases supplied with MATPOWER so I assume it is not in error.


Thanks,

Alastair

________________________________
From: [email protected] 
<[email protected]> on behalf of Abhyankar, Shrirang 
G. <[email protected]>
Sent: 01 August 2014 03:39
To: MATPOWER discussion forum
Cc: MATPOWER discussion forum
Subject: Re: Dispatchable loads with negative reactive demand



On Jul 31, 2014, at 9:17 AM, "HEGGIE Alastair" 
<[email protected]<mailto:[email protected]>> wrote:


Dear all,


Does anyone know if it is possible to convert a load to a dispatchable load if 
the load at a bus has negative reactive demand (and positive real demand)?

You can model it as a generator in MatPower with a negative Pmin, Pmax and a 
positive Qmin, Qmax. What kind of load is this???

Shri


For example, buss 9 in the 39 bus example, case39.m has a reactive demand of 
-66.6. Setting Qmin to -66.6 would not model this correctly but If I set Qmin 
to 66.6 and Qmax to 0 the OPF does not solve. If I set Qmin to 0 and Qmax to 
66.6 I don't think matpower recognizes this as a dispatchable load.

?

Many thanks,


Alastair Heggie

The University of Edinburgh is a charitable body, registered in
Scotland, with registration number SC005336.

Attachment: case39.m
Description: case39.m

Reply via email to