MATPOWER treats generators with PMAX == 0 and PMIN < 0 as dispatchable loads 
and constrains their power factor. It should work with positive or negative 
reactive power consumption. Just make sure QMAX > QMIN.

  Ray


On Aug 1, 2014, at 6:41 AM, HEGGIE Alastair <[email protected]> wrote:

> ​Hi Shri,
> 
> >You can model it as a generator in MatPower with a negative Pmin, Pmax and a 
> >positive Qmin, Qmax.
> 
> My thought was that if I do this Matpower won't recognize it as a 
> dispatchable load and hence won't maintain a constant power factor - perhaps 
> I'm mistaken here, I'll gave it a go though and it seems to be working.
> 
> >What kind of load is this???​
> 
> Honestly, I don't know. See the load at bus 9 in the attached model. It is 
> one of the test cases supplied with MATPOWER so I assume it is not in error.
> 
> Thanks,
> Alastair
> From: [email protected] 
> <[email protected]> on behalf of Abhyankar, Shrirang 
> G. <[email protected]>
> Sent: 01 August 2014 03:39
> To: MATPOWER discussion forum
> Cc: MATPOWER discussion forum
> Subject: Re: Dispatchable loads with negative reactive demand
>  
> 
> 
> On Jul 31, 2014, at 9:17 AM, "HEGGIE Alastair" <[email protected]> wrote:
> 
>> Dear all,
>> 
>> Does anyone know if it is possible to convert a load to a dispatchable load 
>> if the load at a bus has negative reactive demand (and positive real demand)?
> You can model it as a generator in MatPower with a negative Pmin, Pmax and a 
> positive Qmin, Qmax. What kind of load is this???
> 
> Shri
>> 
>> For example, buss 9 in the 39 bus example, case39.m has a reactive demand of 
>> -66.6. Setting Qmin to -66.6 would not model this correctly but If I set 
>> Qmin to 66.6 and Qmax to 0 the OPF does not solve. If I set Qmin to 0 and 
>> Qmax to 66.6 I don't think matpower recognizes this as a dispatchable load.
>> ​
>> Many thanks,
>> 
>> Alastair Heggie
>> The University of Edinburgh is a charitable body, registered in
>> Scotland, with registration number SC005336.
> <case39.m>