Is the output of the generator around 87.5 MW? The total injection from the branches should equal the net load at the bus (load minus the generation), right?
Ray > On Dec 10, 2014, at 12:58 AM, Bijay Hughes <[email protected]> wrote: > > Yes, Shri, I have a generator at bus 4. Could you please tell me where I am > missing the point? > > Thank you. > > On Wed, Dec 10, 2014 at 9:57 AM, Abhyankar, Shrirang G. <[email protected] > <mailto:[email protected]>> wrote: > Do you have a generator at bus 4? > > > On Dec 9, 2014, at 7:31 PM, "Bijay Hughes" <[email protected] > > <mailto:[email protected]>> wrote: > > > > Hello Matpower Users, > > > > I am having some problems understanding bus data versus branch data. Under > > the bus data, I have for example for bus 4, load of 100 MW. However, when I > > investigate the branch data, the power flow to bus 4 from other branches > > only equals like 12.5 MW. Meaning, power flows as follows: > > > > From To Injection (MW) > > 1 4 7.0 > > 3 4 5.5 > > > > I don't understand this. Is it due to loses in the conversion? If so, how > > can the loss (87.5 MW) be so much? Or am I missing a fundamental point > > here? I am stuck and I hope someone can help me. > > > > Sincerely, BH > > > > > > >