Is the output of the generator around 87.5 MW? The total injection from the 
branches should equal the net load at the bus (load minus the generation), 
right?

   Ray

> On Dec 10, 2014, at 12:58 AM, Bijay Hughes <[email protected]> wrote:
> 
> Yes, Shri, I have a generator at bus 4. Could you please tell me where I am 
> missing the point?
> 
> Thank you.
> 
> On Wed, Dec 10, 2014 at 9:57 AM, Abhyankar, Shrirang G. <[email protected] 
> <mailto:[email protected]>> wrote:
> Do you have a generator at bus 4?
> 
> > On Dec 9, 2014, at 7:31 PM, "Bijay Hughes" <[email protected] 
> > <mailto:[email protected]>> wrote:
> >
> > Hello Matpower Users,
> >
> > I am having some problems understanding bus data versus branch data. Under 
> > the bus data, I have for example for bus 4, load of 100 MW. However, when I 
> > investigate the branch data, the power flow to bus 4 from other branches 
> > only equals like 12.5 MW. Meaning, power flows as follows:
> >
> > From   To  Injection (MW)
> > 1           4      7.0
> > 3           4      5.5
> >
> > I don't understand this. Is it due to loses in the conversion? If so, how 
> > can the loss (87.5 MW) be so much? Or am I missing a fundamental point 
> > here? I am stuck and I hope someone can help me.
> >
> > Sincerely, BH
> >
> >
> 
> 
> 