Hi Ray and Shri,

Thanks so much. I solved my problem :D
Take care, Hughes

On Fri, Dec 12, 2014 at 1:29 AM, Ray Zimmerman <[email protected]> wrote:
>
> Is the output of the generator around 87.5 MW? The total injection from
> the branches should equal the net load at the bus (load minus the
> generation), right?
>
>    Ray
>
> On Dec 10, 2014, at 12:58 AM, Bijay Hughes <[email protected]>
> wrote:
>
> Yes, Shri, I have a generator at bus 4. Could you please tell me where I
> am missing the point?
>
> Thank you.
>
> On Wed, Dec 10, 2014 at 9:57 AM, Abhyankar, Shrirang G. <
> [email protected]> wrote:
>
>> Do you have a generator at bus 4?
>>
>> > On Dec 9, 2014, at 7:31 PM, "Bijay Hughes" <[email protected]>
>> wrote:
>> >
>> > Hello Matpower Users,
>> >
>> > I am having some problems understanding bus data versus branch data.
>> Under the bus data, I have for example for bus 4, load of 100 MW. However,
>> when I investigate the branch data, the power flow to bus 4 from other
>> branches only equals like 12.5 MW. Meaning, power flows as follows:
>> >
>> > From   To  Injection (MW)
>> > 1           4      7.0
>> > 3           4      5.5
>> >
>> > I don't understand this. Is it due to loses in the conversion? If so,
>> how can the loss (87.5 MW) be so much? Or am I missing a fundamental point
>> here? I am stuck and I hope someone can help me.
>> >
>> > Sincerely, BH
>> >
>> >
>>
>>
>>
>
>