rem

On Tue, Feb 24, 2015 at 2:03 AM, #ZHANG TIAN# <[email protected]>
wrote:

>  Hello!
>
>
>
> Yes, by changing the LV impedances I can get the correct results. This is
> worth noting that the data in the “Model Explorer” in PowerWorld Simulator
> is in per unit based on the whole system, rather than its real value.
>
>
>
> Many thanks.
>
>
>
> Tian
>
>
>
> *From:* [email protected] [mailto:
> [email protected]] *On Behalf Of *Carlos E
> Murillo-Sanchez
> *Sent:* Monday, February 23, 2015 22:56
> *To:* MATPOWER discussion forum
> *Subject:* Re: Convergence Issue for Distribution Network Power Flow
> Analysis
>
>
>
> Hi;
>
> You have used the TAP column of the branch table to indicate two
> transformers with a 55:1 ratio, and then you used the LV impedances, I
> think, still in PU with a base voltage of 22KV; they are pretty large.  The
> TAP column should be used to specify small variations about 1.0 for true
> tap-changing transformers.  All branch impedances should be specified using
> a single pu system.   I believe that the following is what you are actually
> trying to run:
>
> define_constants;
> mpc = loadcase('caseSG');
> mpc.branch(3:end, BR_R:BR_X) = mpc.branch(3:end, BR_R:BR_X) / 55^2;
> mpc.branch(3:4, TAP) = 0;
> runpf(mpc);
>
> #ZHANG TIAN# wrote:
>
> Dear All,
>
>
>
> I am using Matpower for a distribution network power flow analysis.
>
>
>
> The data I used are taken from a real network, and the network is working
> fine using PowerWorld simulator. Basically, it is a radial network with 14
> buses. Bus 1 is the connection point to the main grid, which I modelled it
> as a slack bus (type 3).
>
>
>
> However, when converting the model into a Matpower case, I can only get a
> failure notification “Did NOT converge (0.01 seconds)”.
>
>
>
> Does anyone have any idea about what might be the problem? Or what are the
> options for me to debug?
>
>
>
> I attached my case data in this email for your reference.
>
>
>
> Thank you all very much.
>
>
>
> Best regards,
>
> Tian
>
>
>
>
>

Reply via email to