No. The loads, PD and QD, are NOT in p.u., they are in MW and MVAr. Check the 
documentation for caseformat or Table B-1 in the User’s Manual 
<http://www.pserc.cornell.edu/matpower/manual.pdf>.

   Ray


> On Feb 24, 2015, at 7:32 AM, mohammad reza Andervazh <[email protected]> 
> wrote:
> 
> Please make sure that the loads i.e. PD and QD in mpc.bus are in p.u.
> Run the program again. It'll works.
> good luck.
> 
> Andervazh
> 
> 
> On Tue, Feb 24, 2015 at 1:09 PM, Carlos Gonzalez Almeida 
> <[email protected] <mailto:[email protected]>> wrote:
> rem
> 
> 
> On Tue, Feb 24, 2015 at 2:03 AM, #ZHANG TIAN# <[email protected] 
> <mailto:[email protected]>> wrote:
> Hello!
> 
>  
> 
> Yes, by changing the LV impedances I can get the correct results. This is 
> worth noting that the data in the “Model Explorer” in PowerWorld Simulator is 
> in per unit based on the whole system, rather than its real value.
> 
>  
> 
> Many thanks.
> 
>  
> 
> Tian
> 
>  
> 
> From: [email protected] 
> <mailto:[email protected]> 
> [mailto:[email protected] 
> <mailto:[email protected]>] On Behalf Of Carlos E 
> Murillo-Sanchez
> Sent: Monday, February 23, 2015 22:56
> To: MATPOWER discussion forum
> Subject: Re: Convergence Issue for Distribution Network Power Flow Analysis
> 
>  
> 
> Hi;
> 
> You have used the TAP column of the branch table to indicate two transformers 
> with a 55:1 ratio, and then you used the LV impedances, I think, still in PU 
> with a base voltage of 22KV; they are pretty large.  The TAP column should be 
> used to specify small variations about 1.0 for true tap-changing 
> transformers.  All branch impedances should be specified using a single pu 
> system.   I believe that the following is what you are actually trying to run:
> 
> define_constants;
> mpc = loadcase('caseSG');
> mpc.branch(3:end, BR_R:BR_X) = mpc.branch(3:end, BR_R:BR_X) / 55^2;
> mpc.branch(3:4, TAP) = 0;
> runpf(mpc);
> 
> #ZHANG TIAN# wrote:
> 
> Dear All,
> 
>  
> 
> I am using Matpower for a distribution network power flow analysis.
> 
>  
> 
> The data I used are taken from a real network, and the network is working 
> fine using PowerWorld simulator. Basically, it is a radial network with 14 
> buses. Bus 1 is the connection point to the main grid, which I modelled it as 
> a slack bus (type 3).
> 
>  
> 
> However, when converting the model into a Matpower case, I can only get a 
> failure notification “Did NOT converge (0.01 seconds)”.
> 
>  
> 
> Does anyone have any idea about what might be the problem? Or what are the 
> options for me to debug?
> 
>  
> 
> I attached my case data in this email for your reference.
> 
>  
> 
> Thank you all very much.
> 
>  
> 
> Best regards,
> 
> Tian
> 
>  
> 
>  
> 
> 
> 

Reply via email to