I hadn't thought of limiting the mpc.gen(wind_farm,10) to be equal to 
mpc.gen(wind_farm,9). Previously I had mpc.gen(wind_farm,10)=0 , so when wind 
output was higher than the total load, simply results.gen(wind_farm,2) was 
almost equal to the total load, and the rest of the wind output was curtailed.
Now I tried  mpc.gen(wind_farm,10)= mpc.gen(wind_farm,9) so in the results, the 
slack bus  absorbs the remaining wind power , having a negative output. However 
the opf does not converge, and I am sure that this is because of voltage issues.
I have tried to- increase Qmin and Qmax limits  (both of the wind farm and the 
slack bus), -I have tried relaxing the voltage limits (in the mpc.bus(:,12) and 
mpc.bus(:,13)-step down the transformer in the slack bus (by  changing the 
value of mpc.branch(branch of the transformer 33/11kv, 9)). But still I cannot 
succeed convergence.
What more could I try?

From: [email protected]
Subject: Re: how power can be absorbed by the slack bus
Date: Mon, 23 Mar 2015 12:00:53 -0400
To: [email protected]

Have you simply tried it? I can’t think of any reason that a negative output 
from the slack bus should cause problems.
   Ray


On Mar 20, 2015, at 1:32 PM, angelina sirri <[email protected]> wrote:Dear 
all,
I am trying to simulate active network management in distribution network in 
11kv.  I have a distribution network with 40 nodes. Of those, one node is the 
distribution substation node, which is also the slack bus, and also I have in 
another node a wind farm.The rest of the nodes are loads. For the cases that I 
have a low demand and a wind power output higher than that, I would like to let 
the wind farm inject that power back to the main network (which I do not 
neither include in the mpc. case , nor simulate).For example, let's say that I 
have the following:sum(mpc.bus(:,3))=5MW;   %total active demand 
sum(mpc.bus(:,4))=4MVar;   %total reactive demand
mpc.gen(slack bus,9)=20MW; %maximum slack bus outputmpc.gen(wind_farm,9)=10MW;  
%maximum wind power output
So in this case, the wind farm is able to feed the rest of the network, with 
zero power taken from the slack bus (if with opf, wind generator is cheaper 
than the slack).How could I feed the remaining 5MW (10-5) from the wind farm 
back to the grid, getting in the results sth like:results.gen(slack bus,2)=-5MW?
I guess that I will have voltage issues, but in first place I was wandering how 
this could happen in case I do not have voltage issues. Afterwards, to face the 
voltage issues I was thinking to manually change the tap of the transformer 
behind the slack like that:
mpc.branch(branch of the transformer 33/11kv, 9) =  range between 0 to 1;
Any proposal would really help!!Kind Regards,Angelina

                                          