See my discussion of “slack” vs. “voltage angle reference” here …

   http://www.mail-archive.com/matpower-l%40cornell.edu/msg02149.html

For the OPF, you still need the latter.

— Ray
 

> On Mar 24, 2015, at 12:38 PM, angelina sirri <[email protected]> wrote:
> 
> I solved it. It was a silly thing. I had Pmin of the source bus equal to 
> zero, so that was the reason, that the opf could not converge for negative 
> output. I changed the Pmin limits of the source to equal to '-(total wind 
> generation)' and it converges properly! I apologize for that. 
> 
> However, as far as the slack bus when I run an opf, If I change the slack bus 
> to a generator bus and run an opf I receive the following error: 
> 
> Attempted to access Varefs(1); index out of
> bounds because numel(Varefs)=0.
> 
> Error in mipsopf_solver (line 120)
>     x0(vv.i1.Va:vv.iN.Va) = Varefs(1);  %% angles
>     set to first reference angle
> 
> Error in opf_execute (line 91)
>       [results, success, raw] =
>       mipsopf_solver(om, mpopt);
> 
> Error in opf (line 225)
> [results, success, raw] = opf_execute(om, mpopt);
> 
> Error in runopf (line 96)
> [r, success] = opf(casedata, mpopt);
> 
> Could you please explain me why is this happening?
> 
> Regards,
> Angelina
> 
> From: [email protected] <mailto:[email protected]>
> Subject: Re: how power can be absorbed by the slack bus
> Date: Tue, 24 Mar 2015 10:18:11 -0400
> To: [email protected] <mailto:[email protected]>
> 
> I didn’t realize you were using an OPF. Since you mentioned a slack bus, I 
> assumed you were using a simple power flow. The OPF does not have a concept 
> of slack (only a voltage angle reference).
> 
> You could try setting VMIN and VMAX equal to the set-point voltage (the 
> corresponding generator’s VG) for your source and wind gen buses and then 
> completely eliminating the reactive power limits for both source and wind gen 
> and the voltage limits at all other buses by setting the mins to –Inf and the 
> maxes to +Inf. Also, make sure you do not have binding branch flow limits, by 
> setting RATE_A to zero everywhere.
> 
> If this still doesn’t work, try reducing PMAX of the wind generator until it 
> does. I assume you’ve confirmed that you can solve the case when the wind 
> generator is not producing, correct?
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> B30 Warren Hall, Cornell University, Ithaca, NY 14853  USA
> phone: (607) 255-9645
> 
> On Mar 23, 2015, at 3:18 PM, angelina sirri <[email protected] 
> <mailto:[email protected]>> wrote:
> 
> I hadn't thought of limiting the mpc.gen(wind_farm,10) to be equal to 
> mpc.gen(wind_farm,9).
>  Previously I had mpc.gen(wind_farm,10)=0 , so when wind output was higher 
> than the total load, simply results.gen(wind_farm,2) was almost equal to the 
> total load, and the rest of the wind output was curtailed.
> 
> Now I tried  mpc.gen(wind_farm,10)= mpc.gen(wind_farm,9) so in the results, 
> the slack bus  absorbs the remaining wind power , having a negative output. 
> However the opf does not converge, and I am sure that this is because of 
> voltage issues.
> 
> I have tried to
> - increase Qmin and Qmax limits  (both of the wind farm and the slack bus), 
> -I have tried relaxing the voltage limits (in the mpc.bus(:,12) and 
> mpc.bus(:,13)
> -step down the transformer in the slack bus (by  changing the value of 
> mpc.branch(branch of the transformer 33/11kv, 9)). But still I cannot succeed 
> convergence.
> 
> What more could I try?
> 
> From: [email protected] <mailto:[email protected]>
> Subject: Re: how power can be absorbed by the slack bus
> Date: Mon, 23 Mar 2015 12:00:53 -0400
> To: [email protected] <mailto:[email protected]>
> 
> Have you simply tried it? I can’t think of any reason that a negative output 
> from the slack bus should cause problems.
> 
>    Ray
> 
> 
> On Mar 20, 2015, at 1:32 PM, angelina sirri <[email protected] 
> <mailto:[email protected]>> wrote:
> 
> Dear all,
> 
> I am trying to simulate active network management in distribution network in 
> 11kv.  I have a distribution network with 40 nodes. Of those, one node is the 
> distribution substation node, which is also the slack bus, and also I have in 
> another node a wind farm.The rest of the nodes are loads.
>  For the cases that I have a low demand and a wind power output higher than 
> that, I would like to let the wind farm inject that power back to the main 
> network (which I do not neither include in the mpc. case , nor simulate).
> For example, let's say that I have the following:
> sum(mpc.bus(:,3))=5MW;   %total active demand 
> sum(mpc.bus(:,4))=4MVar;   %total reactive demand
> 
> mpc.gen(slack bus,9)=20MW; %maximum slack bus output
> mpc.gen(wind_farm,9)=10MW;  %maximum wind power output
> 
> So in this case, the wind farm is able to feed the rest of the network, with 
> zero power taken from the slack bus (if with opf, wind generator is cheaper 
> than the slack).
> How could I feed the remaining 5MW (10-5) from the wind farm back to the 
> grid, getting in the results sth like:
> results.gen(slack bus,2)=-5MW?
> 
> I guess that I will have voltage issues, but in first place I was wandering 
> how this could happen in case I do not have voltage issues. Afterwards, to 
> face the voltage issues I was thinking to manually change the tap of the 
> transformer behind the slack like that:
> 
> mpc.branch(branch of the transformer 33/11kv, 9) =  range between 0 to 1;
> 
> Any proposal would really help!!
> Kind Regards,
> Angelina

Reply via email to