Yes, thanks, Jose. I’ve added another item to FAQ #5 with links to your posts.

   Ray


> On Aug 16, 2015, at 11:03 PM, Abhyankar, Shrirang G. <abhy...@anl.gov> wrote:
> 
> Thank you.
> 
> On Aug 15, 2015, at 12:06 PM, "Jose Luis Marin" <mari...@gridquant.com 
> <mailto:mari...@gridquant.com>> wrote:
> 
>> Sure, of course I have no problem with that.
>> 
>> Also, I realized I missed one detail:  if there were any phase-shifters in 
>> the network, I would also (initially) set their phase-shifts to zero.  That 
>> way you would obtain a truly "pure reactive" network.  Then, when you work 
>> your way ramping up real power, you would also want to ramp those 
>> phase-shifts back to their original values as well.
>> 
>> -- 
>> Jose L. Marin
>> Gridquant España SL
>> Grupo AIA
>> 
>> 
>> On Fri, Aug 14, 2015 at 10:17 PM, Abhyankar, Shrirang G. <abhy...@anl.gov 
>> <mailto:abhy...@anl.gov>> wrote:
>> Jose,
>>   Would it be fine with you if the steps you’ve mentioned below are added to 
>> MATPOWER FAQ#5 http://www.pserc.cornell.edu//matpower/#pfconvergence 
>> <http://www.pserc.cornell.edu//matpower/#pfconvergence>  Many a times, 
>> useful and detailed suggestions, such as what you’ve enumerated, get lost in 
>> email exchanges and someone trying to pull up this information has to resort 
>> to digging it out of the archive. It’ll be good to have your steps up on the 
>> FAQ.
>> 
>> Thanks,
>> Shri  
>> 
>> From: Jose Luis Marin <mari...@gridquant.com <mailto:mari...@gridquant.com>>
>> Reply-To: MATPOWER discussion forum <matpowe...@list.cornell.edu 
>> <mailto:matpowe...@list.cornell.edu>>
>> Date: Wednesday, August 12, 2015 at 2:42 AM
>> To: MATPOWER discussion forum <matpowe...@list.cornell.edu 
>> <mailto:matpowe...@list.cornell.edu>>
>> Subject: Re: convergence problem in runpf.
>> 
>> Mirish,
>> 
>> I couldn't help notice that you're building this model from scratch (well, 
>> from a database) and you mentioned "To make the problem simple I used all 
>> buses as PQ buses except one slack bus".   This actually makes it harder to 
>> converge, unless you have *very* accurate data on what the reactive 
>> injections Q (on generator buses) should be.
>> 
>> May I suggest a different, incremental approach:
>> Start by keeping all generator buses you can as PV, instead of PQ. They will 
>> help holding up the voltage profile.  After all, a PV node is a slack bus in 
>> what regards the reactive power injection.
>> For the loads, start by zeroing out PD (real power demand), but keeping QD 
>> (reactive demand)
>> For generators, set the scheduled PG to zero
>> For lines & transformers, zero out the resistance R
>> The resulting network will be a "purely reactive power" model. Now run a 
>> powerflow.  If this doesn't have a feasible powerflow solution, it is 
>> because some branches have an X parameter that is too large (or 
>> equivalently, some load QD is too large).  Ramp down the profile of QD until 
>> you see convergence.
>> Look at the resulting Q flows across branches, and try to detect anomalously 
>> large values (i.e. clear outliers). They will help you uncover values of X 
>> that may be wrong (too large).  Also, keep an eye on negative X coming from 
>> equivalents such as 3-winding transformers; they may also be wrong.
>> Once you get that working, ramp up the values of PD on loads and PG on 
>> generators (keeping an eye on the swing's resulting PG, in order to 
>> redistribute big excesses).
>> Finally ramp up the resistance on lines.
>> The whole idea is based on the fact that, for transmission networks (lines 
>> with R<<X), the reactive flows are like the "backbone" on which real power 
>> flows can sort of "ride on".  Get a healthy backbone first, and then you can 
>> start transporting real power.
>> 
>> Hope it helps,
>> 
>> -- 
>> Jose L. Marin
>> Gridquant España SL
>> Grupo AIA
>> 
>> 
>> On Wed, Aug 12, 2015 at 2:36 AM, Mirish Thakur <mirishtha...@gmail.com 
>> <mailto:mirishtha...@gmail.com>> wrote:
>> Dear Mr.Shree,
>> 
>> Thank you very much for your help. As per your suggestion and FAQ I tried to 
>> find out the problems.
>> The results I got-
>> 1) Fast-decoupled power flow did not converge in 30 iterations.
>> 2) By following   http://www.pserc.cornell.edu/matpower/#pfconvergence 
>> <http://www.pserc.cornell.edu/matpower/#pfconvergence>  I tried to runcpf to 
>> get good  initial guess and i got results like 
>> step   1 : lambda =  0.084, corrector did not converge in 10 iterations. 
>> Where lambda is < 1 and for reducing steady state loading limitation I 
>> reduced demand less than 60 % which also failed to converge the power flow.
>> 3) Also I tried to run an optimal power flow according to Dr. Ray's 
>> explanation  given in following link-
>> 
>> https://www.mail-archive.com/search?l=matpower-l@cornell.edu&q=subject:%22Re%5C%3A+%5C%5BMatpower%5C%5D+3500+bus+simulation%22&o=newest
>>  
>> <https://www.mail-archive.com/search?l=matpower-l@cornell.edu&q=subject:%22Re%5C%3A+%5C%5BMatpower%5C%5D+3500+bus+simulation%22&o=newest>
>> 
>> but got the results like-
>> 
>> MATPOWER Version 5.1, 20-Mar-2015 -- AC Optimal Power Flow
>> MATLAB Interior Point Solver -- MIPS, Version 1.2, 20-Mar-2015
>>  (using built-in linear solver)
>>  it    objective   step size   feascond     gradcond     compcond     
>> costcond  
>> ----  ------------ --------- ------------ ------------ ------------ 
>> ------------
>>   0     1200199.7                 2.41677         0.71      536.762          
>>   0
>>   1     946197.39     15.531       1.3682      1.75871      525.914     
>> 0.209885
>>   2     954529.91     15.405     0.766107     0.203773      297.341   
>> 0.00871422
>>   3      954849.8     12.849     0.727712    0.0545952      258.471   
>> 0.00033166
>>   4     954629.03      13035      0.69114     0.107402      258.048  
>> 0.000228815
>>   5     954614.88      33406     0.692682     0.255673      257.828  
>> 1.46744e-05
>>   6     954525.69      14111     0.579613     0.143897      256.765  
>> 9.24569e-05
>>   7     954539.42      61648     0.581139     0.501345      255.994  
>> 1.42362e-05
>>   8     954518.93      22452     0.573652     0.478609      255.465  
>> 2.12443e-05
>>   9     954494.92     8540.4     0.556318     0.403754      254.653  
>> 2.48944e-05
>>  10     954523.58      20366     0.556265     0.570707      254.104  
>> 2.97206e-05
>>  11     954522.07     6142.4     0.554989     0.647881      256.561  
>> 1.57288e-06
>>  12     954573.42     6192.9     0.513972     0.716706      253.604  
>> 5.32434e-05
>>  13     954575.97     5912.1     0.509457     0.699751      252.612  
>> 2.64406e-06
>>  14     954576.23      16534     0.509454     0.674865      253.278  
>> 2.64555e-07
>>  15     954579.65      12324     0.509394     0.812237      252.966  
>> 3.54362e-06
>>  16     954579.86     7650.3     0.509391      0.80973      252.948  
>> 2.18359e-07
>>  17     954579.87     8185.1     0.509391     0.809591      252.947  
>> 1.48635e-08
>>  18     954579.88     8696.2     0.509391     0.809411      252.945  
>> 1.31087e-08
>>  19      954579.9     9392.5      0.50939      0.80927      252.943   
>> 1.3818e-08
>> Numerically Failed
>> 
>> Did not converge in 19 iterations.
>> 
>> >>>>>  Did NOT converge (3.71 seconds)  <<<<<
>> 
>> 4) But when I used spy(J) , to look jacobian matrix it gives me some strange 
>> distribution. Herewith I attached image of jacobian matrix. ( I have modeled 
>> transmission lines and transformers to get one single branch matrix e.g. 
>> branch_matrix=vertcat(transmission_lines,grid_transformer) which is similar 
>> to matpower test cases.). So could you please suggest me what necessary 
>> steps I should follow?
>> Thank you for your time.
>> 
>> Regards
>> Mirish Thakur
>> KIT, University.
>> 
>> On Mon, Aug 10, 2015 at 7:14 PM, Abhyankar, Shrirang G. <abhy...@anl.gov 
>> <mailto:abhy...@anl.gov>> wrote:
>> I would suggest trying the following:
>> 
>> Use the solution of a fast decoupled power flow or an optimal power flow 
>> (with line limits and voltage limits relaxed) as the initial guess for the 
>> power flow.
>> Follow step 5 in http://www.pserc.cornell.edu/matpower/#pfconvergence 
>> <http://www.pserc.cornell.edu/matpower/#pfconvergence> making CPF to stop 
>> when the nose-point is reached. This can be done via results = 
>> runcpf(mpcbase,mpctarget,mpoption(‘cpf.stop_at’,’NOSE’)). If 
>> results.cpf.max_lam is >= 1, then it shows that the initial guess for the 
>> power flow is the problem for its divergence. To obtain a ‘good’ initial 
>> guess, run the continuation power flow again making it to stop exactly at 
>> lam = 1 (the target case loading and generation) via results = 
>> runcpf(mpcbase,mpctarget,mpoption(‘cpf.stop_at’,1.0)). You can then save the 
>> results struct as a matpower case file (via savecase()). On the other hand, 
>> if results.cpf.max_lam < 1, then the loading/generation in your original 
>> case is beyond the system steady-state loading limit.
>> Shri
>> From: Mirish Thakur <mirishtha...@gmail.com <mailto:mirishtha...@gmail.com>>
>> Reply-To: MATPOWER discussion forum <matpowe...@list.cornell.edu 
>> <mailto:matpowe...@list.cornell.edu>>
>> Date: Monday, August 10, 2015 at 10:44 AM
>> To: MATPOWER discussion forum <matpowe...@list.cornell.edu 
>> <mailto:matpowe...@list.cornell.edu>>
>> Subject: convergence problem in runpf.
>> 
>> Dear Matpower Community,
>> 
>> 
>> 
>> I’m working on power flow project and have used grid data from database. I 
>> have modelled all line parameters (R X B) in p.u. system, also same for 
>> transformers and kept generator output until it satisfies active and 
>> reactive  power demand. For renewable generation, I specified as negative 
>> demand on respective buses. I checked all possibilities mentioned in  FAQ 
>> (http://www.pserc.cornell.edu/matpower/#pfconvergence 
>> <http://www.pserc.cornell.edu/matpower/#pfconvergence> ) but couldn’t figure 
>> out problem. Also I checked (case_info) to see any island but got full 
>> system without island. To make the problem simple I used all buses as PQ 
>> buses except one slack bus. Also my casefile converges for rundcpf but fails 
>> to runpf and gives error like ‘Newton's method power flow did not converge 
>> in 10 iterations.’ Also I found that when I use following code-
>> 
>> 
>> 
>>      opt  = mpoption('OUT_BUS', 0, 'OUT_BRANCH', 0, 'VERBOSE', 2);
>> 
>>    mpc  = loadcase('casefile');
>> 
>>  results =runpf(mpc,opt); 
>> 
>> 
>> may be it gives me divergence of PQ mismatch instead of convergence.
>> 
>> 
>> 
>> MATPOWER Version 5.1, 20-Mar-2015 -- AC Power Flow (Newton)
>> 
>>  
>>  it    max P & Q mismatch (p.u.)
>> 
>> ----  ---------------------------
>> 
>>   0         2.296e+01
>> 
>>   1         1.729e+01
>> 
>>   2         2.450e+03
>> 
>>   3         2.352e+03
>> 
>>   4         6.962e+06
>> 
>>   5         1.740e+06
>> 
>>   6         4.352e+05
>> 
>>   7         1.753e+07
>> 
>>   8         4.382e+06
>> 
>>   9         3.322e+06
>> 
>>  10         8.303e+05
>> 
>> Newton's method power flow did not converge in 10 iterations.
>> 
>>  
>> >>>>>  Did NOT converge (0.23 seconds)  <<<<<
>> 
>>  
>>  
>> results =
>> 
>>         version: '2'
>> 
>>     baseMVA: 100
>> 
>>              bus: [1086x13 double]
>> 
>>              gen: [467x21 double]
>> 
>>          branch: [2145x17 double]
>> 
>>             order: [1x1 struct]
>> 
>>                 et: 0.2320
>> 
>>        success: 0
>> 
>> I will be very thankful for your help.
>> 
>> 
>> Regards 
>> 
>> Mirish Thakur.
>> 
>> KIT, University.
>> 
>> 
>> 
>> 