I assume you mean that you also set QC1MIN = 0, QC1MAX = 0, QC2MAX = 4.84 and
QC2MIN = -3.28?
If so, then I’m not sure where you are getting the 0.24 MVAr. The allowable
range at 10 MW would be -3.28 to +4.84 MVAr … at 9.5 MW it would be 0.95 times
those numbers, i.e. -3.12 to +4.60 MVAr.
Which is what you see.
Ray
> On Apr 6, 2016, at 11:16 AM, Mirish Thakur <[email protected]> wrote:
>
> Dear Prof. Ray,
>
> I have modeled capability curve in triangular shape. Ex. P1=0, P2= 10 MW,
> Qmax =4.84, Qmin =-3.28, Pmax=Pmin=9.5. So at this Pmax limit generator
> should produce reactive power =0.24 MVAr but in opf it generates 4.60 MVAr. I
> don't understand the reason because I have fixed the active power generation
> and Qg should generate from zero to vertical max limit of capability curve.
> I read previous answers on forum
> https://www.mail-archive.com/matpower-l%40cornell.edu/msg03986.html
> <https://www.mail-archive.com/matpower-l%40cornell.edu/msg03986.html> but
> could not understand what changes you have made in hasPQcap function. Thank
> you for your time.
>
> regards
> Mirish