Hi,

@ Jose L. Marin:
I used a generator in both cases, hence it should be the correct sign (should result in the same I guess). Anyway P was very small, around 1e-6 MW.

I'm not sure if I've modelled something wrong: S_base is 100, my generator is at bus 1 (at the end zeros(1,12)): bus Pg Qg Qmax Qmin Vg mBase status Pmax ... 1 0.4 0 0.7 -0.45 1.04 100 1 1.3 ...

And the PQ-bus:
bus_i type Pd Qd Gs Bs area Vm Va baseKV zone Vmax Vmin 246 1 2.64e-06 -30 0 0 3 1 0 20 4 2 0.6;

I've tried another thing: I changed the PQ-bus from -30 to +30 Mvar (e.g. mpc.bus(1, 4) = 0) and for another time I did the same with the generator from +30 to -30 Mvar (e.g. mpc.gen(1, 3)=30), the other part (gen vs. load) was always set to 0. The result was not (!) the same... hm? - I guess this is the reason for the problem. With the bus I get results from -8 Mvar up to 30 Mvar with v=0.635 to 1.46 whereas with the generator the voltage varies only within -1 Mvar and +1 Mvar (appr. 1.01 pu to appr. 1.04 pu), for other Q-injections the voltage doesn't change.

I uploaded the plot under: http://de.tinypic.com/r/350pk02/9

Do you have any idea why?

Thanks for your help, nice regards,
Chris



Am 28.04.2016 um 17:41 schrieb Jose Luis Marin:

Those are certainly some crazy Mvar injections! Just checking: are you sure you reversed the signs of P properly when switching the type of that bus from PQ (load) to PV (gen with neg real power), also taking care of making the corresponding changes in the bus row and adding a new gen row?

If you could share your case file I could try to give you a quick diagnostic.

--
Jose L. Marin
Grupo AIA



On Thu, Apr 28, 2016 at 5:19 PM, Chris Prokop <[email protected] <mailto:[email protected]>> wrote:

    Thanks for your responses.

    @ Ray Zimmerman:
    I can't find the problem here. If I set Q=+0.7 Mvar (cap.), the
    voltage at this bus is about 1.04 p.u., with Q=-0.7 Mvar (ind.) it
    decreases to 1.02 p.u., the power flow converges as expected (+the
    result is as expected). Only converting this bus into a PV-bus
    results in the problem mentioned above (with or without limits). I
    don't get why the Newton Power Flow returns for example 1e3 Mvar
    for this bus as a result, as only <1 Mvar should have been enough
    reactive power.
    Before solving the case the reactive power of the generators at
    the PV-buses are (variable gen in runpf):
    - Reference bus: 0 Mvar
    - PV-Bus1: 0 Mvar
    - PV-Bus2: 64.4 Mvar
    - PV-Bus3 (the problematic one): 0.1 Mvar
    after solving it (after pfsoln), the variable gen is filled with:
    - Reference bus: 1e6 Mvar
    - PV-Bus1: 2.7e4 Mvar
    - PV-Bus2: 9.6e3 Mvar
    - PV-Bus3 (the problematic one): -600 Mvar
    whereas the next most reactive power intensive gen&bus has less
    than 5e2 Mvar. I don't understand where the power comes from/goes
    to...

    @ Jose Luis Marin:
    If I use the voltage from the PQ-calculation (e.g. 20.6668/20
    p.u.) there remains the same problem. Also without Q-limits I get
    the the problem...
    Vg=1 p.u. actually works as a PV-bus, Vg=1.01 or Vg=1.02 etc. don't.
    Nice regards,
    Chris

    2016-04-28 16:04 GMT+02:00 Ray Zimmerman <[email protected]
    <mailto:[email protected]>>:

        It sounds like the voltage at that bus may be very sensitive
        to the reactive power injection. One thing you might try to
        get some idea of this is to change that bus back to PQ with
        the reactive at the lower limit, then try running a few cases
        with slightly perturbed values of the reactive power at that
        generator and see how the voltage at the bus changes.

           Ray


        On Apr 28, 2016, at 8:40 AM, Chris Prokop
        <[email protected]
        <mailto:[email protected]>> wrote:

        Hi,

        I'm using Matpower (v5.0b1, but the same holds for v5.1)
        for a 220 kV/110 kV/20 kV-grid quite a while. The grid has 1
        reference bus (220 kV), 2 PV-buses (220 kV) and >100 PQ-buses
        (110 kV & 20 kV). So far calculating the grid using runpf
        with Newton has never been a problem.

        Now I've tried to change a 20 kV PQ-bus to a PV-bus with the
        Q-limits +0.7 for Q_max and -0.45 for Q_min (considering
        mpopt = mpoption('pf.enforce_q_lims', 1)). If I set Vg of the
        generator to 1.05 I get the error:
        "All 4 remaining gens exceed their Q limits : INFEASIBLE PROBLEM"
        whereas when using 1.00 as Vg there is no problem (then the
        generator is at its lower Q-limit, hence converted to PQ). If
        the problem is infeasible the result of pfsoln in runpf are
        Q-values of all 4 PV generators (Slack+3 PV) that are out of
        their limits. Why is there such a big difference between the
        case V=1.05 and V=1.00?

        As a info: the Slack has a Q-Limit of +-10000, both of the
        already existing PV buses +720/-290, according
        to case_info the total generation is -300 MW+j10 Mvar, the
        total load 300 MW-j50 Mvar, but I've tried several scenarios
        which are no problem when using the PQ instead of the PV-bus
        (or the Vg=1).

        Does anybody experience a similar problem/has an idea how to
        fix it?

        Nice regards,
        Chris