Looking at those records I think I may have misunderstood what you're
doing.  I thought you were converting a given PQ bus (BUS_I=246) into PV,
but the generator record you're showing is attached to BUS_I=1 instead.

To be precise, I thought you were starting from (numbers made up for this
example):

bus_i       type    Pd       Qd      Gs    Bs    area    Vm    Va
baseKV   zone    Vmax   Vmin
246          1      15.37    1.12    0     0     3       1     0
20       4       2      0.6;

And, assuming that the solution for that starting case gave for instance
V=1.0375 on BUS_I=246, then making these changes to the case:

bus_i       type    Pd       Qd      Gs    Bs    area    Vm    Va
baseKV    zone   Vmax   Vmin
246          1      0.0      0.0     0     0     3       1     0
20        4      2      0.6;

plus adding this generator to the bus:
bus        Pg        Qg        Qmax       Qmin       Vg        mBase
status    Pmax   ...
246        -15.37     0         999.99     -999.99    1.0375    100
1       1.3        ...

Then, provided you are not enforcing MVAR limits (which may change a lot of
things), you should obtain the same powerflow solution in this second case
(with Qg near -1.12, in this example),


Did I miss something?


-- 
Jose L. Marin
Grupo AIA



On Thu, Apr 28, 2016 at 7:26 PM, Chris Prokop <[email protected]>
wrote:

> Hi,
>
> @ Jose L. Marin:
> I used a generator in both cases, hence it should be the correct sign
> (should result in the same I guess). Anyway P was very small, around 1e-6
> MW.
>
> I'm not sure if I've modelled something wrong: S_base is 100, my generator
> is at bus 1 (at the end zeros(1,12)):
> bus        Pg        Qg        Qmax        Qmin    Vg        mBase
> status    Pmax   ...
> 1           0.4        0            0.7        -0.45        1.04    100
>     1            1.3        ...
>
> And the PQ-bus:
> bus_i       type    Pd               Qd    Gs    Bs    area    Vm    Va
> baseKV    zone    Vmax    Vmin
> 246          1         2.64e-06    -30    0      0     3          1
> 0     20            4           2           0.6;
>
> I've tried another thing: I changed the PQ-bus from -30 to +30 Mvar (e.g.
> mpc.bus(1, 4) = 0)  and for another time I did the same with the generator
> from +30 to -30 Mvar (e.g. mpc.gen(1, 3)=30), the other part (gen vs. load)
> was always set to 0. The result was not (!) the same... hm? - I guess this
> is the reason for the problem.
> With the bus I get results from -8 Mvar up to 30 Mvar with v=0.635 to 1.46
> whereas with the generator the voltage varies only within -1 Mvar and +1
> Mvar (appr. 1.01 pu to appr. 1.04 pu), for other Q-injections the voltage
> doesn't change.
>
> I uploaded the plot under: http://de.tinypic.com/r/350pk02/9
>
> Do you have any idea why?
>
> Thanks for your help, nice regards,
> Chris
>
>
>
>
> Am 28.04.2016 um 17:41 schrieb Jose Luis Marin:
>
>
> Those are certainly some crazy Mvar injections!  Just checking: are you
> sure you reversed the signs of P properly when switching the type of that
> bus from PQ (load) to PV (gen with neg real power), also taking care of
> making the corresponding changes in the bus row and adding a new gen row?
>
> If you could share your case file I could try to give you a quick
> diagnostic.
>
> --
> Jose L. Marin
> Grupo AIA
>
>
>
> On Thu, Apr 28, 2016 at 5:19 PM, Chris Prokop <[email protected]>
> wrote:
>
>> Thanks for your responses.
>>
>> @ Ray Zimmerman:
>> I can't find the problem here. If I set Q=+0.7 Mvar (cap.), the voltage
>> at this bus is about 1.04 p.u., with Q=-0.7 Mvar (ind.) it decreases to
>> 1.02 p.u., the power flow converges as expected (+the result is as
>> expected). Only converting this bus into a PV-bus results in the problem
>> mentioned above (with or without limits). I don't get why the Newton Power
>> Flow returns for example 1e3 Mvar for this bus as a result, as only <1 Mvar
>> should have been enough reactive power.
>> Before solving the case the reactive power of the generators at the
>> PV-buses are (variable gen in runpf):
>> - Reference bus: 0 Mvar
>> - PV-Bus1: 0 Mvar
>> - PV-Bus2: 64.4 Mvar
>> - PV-Bus3 (the problematic one): 0.1 Mvar
>> after solving it (after pfsoln), the variable gen is filled with:
>> - Reference bus: 1e6 Mvar
>> - PV-Bus1: 2.7e4 Mvar
>> - PV-Bus2: 9.6e3 Mvar
>> - PV-Bus3 (the problematic one): -600 Mvar
>> whereas the next most reactive power intensive gen&bus has less than 5e2
>> Mvar. I don't understand where the power comes from/goes to...
>>
>> @ Jose Luis Marin:
>> If I use the voltage from the PQ-calculation (e.g. 20.6668/20 p.u.) there
>> remains the same problem. Also without Q-limits I get the the problem...
>> Vg=1 p.u. actually works as a PV-bus, Vg=1.01 or Vg=1.02 etc. don't.
>>
>>
>> Nice regards,
>> Chris
>>
>> 2016-04-28 16:04 GMT+02:00 Ray Zimmerman <[email protected]>:
>>
>>> It sounds like the voltage at that bus may be very sensitive to the
>>> reactive power injection. One thing you might try to get some idea of this
>>> is to change that bus back to PQ with the reactive at the lower limit, then
>>> try running a few cases with slightly perturbed values of the reactive
>>> power at that generator and see how the voltage at the bus changes.
>>>
>>>    Ray
>>>
>>>
>>> On Apr 28, 2016, at 8:40 AM, Chris Prokop <[email protected]>
>>> wrote:
>>>
>>> Hi,
>>>
>>>
>>> I'm using Matpower (v5.0b1, but the same holds for v5.1) for a 220
>>> kV/110 kV/20 kV-grid quite a while. The grid has 1 reference bus (220 kV),
>>> 2 PV-buses (220 kV) and >100 PQ-buses (110 kV & 20 kV). So far calculating
>>> the grid using runpf with Newton has never been a problem.
>>>
>>> Now I've tried to change a 20 kV PQ-bus to a PV-bus with the Q-limits
>>> +0.7 for Q_max and -0.45 for Q_min (considering mpopt =
>>> mpoption('pf.enforce_q_lims', 1)). If I set Vg of the generator to 1.05
>>> I get the error:
>>> "All 4 remaining gens exceed their Q limits : INFEASIBLE PROBLEM"
>>> whereas when using 1.00 as Vg there is no problem (then the generator is
>>> at its lower Q-limit, hence converted to PQ). If the problem is infeasible
>>> the result of pfsoln in runpf are Q-values of all 4 PV generators (Slack+3
>>> PV) that are out of their limits. Why is there such a big difference
>>> between the case V=1.05 and V=1.00?
>>>
>>> As a info: the Slack has a Q-Limit of +-10000, both of the already
>>> existing PV buses +720/-290, according to case_info the total generation is
>>> -300 MW+j10 Mvar, the total load 300 MW-j50 Mvar, but I've tried several
>>> scenarios which are no problem when using the PQ instead of the PV-bus (or
>>> the Vg=1).
>>>
>>>
>>> Does anybody experience a similar problem/has an idea how to fix it?
>>>
>>> Nice regards,
>>> Chris
>>>
>>>
>>>
>>
>
>