Hi Nur,
Dont divide R and X with the voltage. I get the following power flow
without those two lines.

------------
runpf('LV10')

MATPOWER Version 6.0b1, 01-Jun-2016 -- AC Power Flow (Newton)

Newton's method power flow converged in 5 iterations.

Converged in 0.02 seconds
================================================================================
|     System Summary
    |
================================================================================

How many?                How much?              P (MW)            Q (MVAr)
---------------------    -------------------  -------------
 -----------------
Buses             12     Total Gen Capacity     261.0        -302.0 to 302.0
Generators        11     On-line Capacity       250.0        -300.0 to 300.0
Committed Gens     1     Generation (actual)      1.2               0.5
Loads             10     Load                     1.0               0.3
  Fixed           10       Fixed                  1.0               0.3
  Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
Shunts             0     Shunt (inj)             -0.0               0.0
Branches          11     Losses (I^2 * Z)         0.23              0.16
Transformers       0     Branch Charging (inj)     -                0.0
Inter-ties         0     Total Inter-tie Flow     0.0               0.0
Areas              1

                          Minimum                      Maximum
                 -------------------------  --------------------------------
Voltage Magnitude   0.717 p.u. @ bus 11         1.000 p.u. @ bus 1
Voltage Angle      -5.40 deg   @ bus 11         0.00 deg   @ bus 1
P Losses (I^2*R)             -                  0.06 MW    @ line 1-2
Q Losses (I^2*X)             -                  0.04 MVAr  @ line 1-2

================================================================================
|     Bus Data
    |
================================================================================
 Bus      Voltage          Generation             Load
  #   Mag(pu) Ang(deg)   P (MW)   Q (MVAr)   P (MW)   Q (MVAr)
----- ------- --------  --------  --------  --------  --------
    1  1.000    0.000*     1.23      0.46       -         -
    2  0.950   -0.744       -         -        0.10      0.03
    3  0.905   -1.483       -         -        0.10      0.03
    4  0.864   -2.206       -         -        0.10      0.03
    5  0.828   -2.898       -         -        0.10      0.03
    6  0.797   -3.541       -         -        0.10      0.03
    7  0.770   -4.116       -         -        0.10      0.03
    8  0.749   -4.607       -         -        0.10      0.03
    9  0.733   -4.993       -         -        0.10      0.03
   10  0.722   -5.260       -         -        0.10      0.03
   11  0.717   -5.397       -         -        0.10      0.03
   12  1.000    0.000       -         -         -         -
                        --------  --------  --------  --------
               Total:      1.23      0.46      1.00      0.30

================================================================================
|     Branch Data
   |
================================================================================
Brnch   From   To    From Bus Injection   To Bus Injection     Loss (I^2 *
Z)
  #     Bus    Bus    P (MW)   Q (MVAr)   P (MW)   Q (MVAr)   P (MW)   Q
(MVAr)
-----  -----  -----  --------  --------  --------  --------  --------
 --------
   1      1      2      1.23      0.46     -1.17     -0.42     0.055
 0.04
   2      2      3      1.07      0.39     -1.03     -0.36     0.046
 0.03
   3      3      4      0.93      0.33     -0.89     -0.30     0.038
 0.03
   4      4      5      0.79      0.27     -0.76     -0.25     0.030
 0.02
   5      5      6      0.66      0.22     -0.64     -0.20     0.023
 0.02
   6      6      7      0.54      0.17     -0.52     -0.16     0.016
 0.01
   7      7      8      0.42      0.13     -0.41     -0.13     0.011
 0.01
   8      8      9      0.31      0.10     -0.30     -0.09     0.006
 0.00
   9      9     10      0.20      0.06     -0.20     -0.06     0.003
 0.00
  10     10     11      0.10      0.03     -0.10     -0.03     0.001
 0.00
  11      1     12      0.00      0.00      0.00      0.00     0.000
 0.00
                                                             --------
 --------
                                                    Total:     0.228
 0.16

On Tue, Oct 25, 2016 at 10:31 PM, Nazurah Nasir <[email protected]>
wrote:

>
>
> Hi all MatPower community,
>
> I am trying to develop a simple LV network in radial network distribution.
> However, my model did not converge or if I scale the R and X, the results
> is too big (which means the R,X) scaling is wrong. I tried for one month
> now but still could get around why it is not converging.
>
> I need to work on this PowerFlow to work inside my bilevel programming
> loop. but it seems my code won't work because the power flow is not
> converging.
>
> I need help on verifying my parameter. Attached is my code that I build.
> As the MatPower is in three phase balanced, I lumped my loads that
> connected to a bus as one load, hence the voltage at the bus is 0.415kV. My
> input power are all in kW, hence I change the impedance values accordingly
> by multiplying it by 1000. The input power is just a dummy value of 0.1MW
> because it will update itself in a loop. But since input power is in kW, I
> should divide that by 1000 right?
>
> Thank you so much for the help.
>
>
> Best regards,
> Nur
>
>

Reply via email to