If you want to do things properly, I guess you would have to do *all* of
the following:

   - First, MATPOWER expects baseMVA to be in MW.  If you want to use a
   p.u. system based around Volts and 1 kW (instead of the traditional kV and
   100 MW), then you need baseMVA=0.001 at the beginning of your case file.
   - Expressing voltages in pu should be no problem, just divide the
   quantity in volts by your voltage levels (in your case I see it's only one,
   415 Volts)
   - Now, MATPOWER expects all power quantities (P, Q) to be expressed in
   MW.  So if your values are in kW, divide them by 1000.
   - Finally, to convert resistances and reactances (R, X), use your
   baseMVA and voltage base as follows: take the initial quantity in Ohms, and
   multiply it by:  baseMVA / Vbase^2 = 1000 Watts / (415 Volts)^2 =
   5.806357961968356e-03
   - You don't have Bshunt values in your case, but if you had, the
   conversion factor would be just the inverse of the one used for resistance
   and  reactance.

I hope I'm not missing anything, I think that's all you need in your case.

-- 
Jose L. Marin
Grupo AIA




2016-10-26 14:44 GMT+02:00 Nazurah Nasir <nurnazu...@gmail.com>:

> But does that means I should not divide my input power data by 1000 to
> make it in MW? If I do that, it won't converge. For example, these are my
> Power input for one time:
>
> Columns 1 through 6
>     1.0000    3.0000         0         0         0         0
>     2.0000    1.0000    0.0012    0.0004         0         0
>     3.0000    1.0000    0.0019    0.0006         0         0
>     4.0000    1.0000    0.0006    0.0002         0         0
>     5.0000    1.0000    0.0024    0.0008         0         0
>     6.0000    1.0000    0.0012    0.0004         0         0
>     7.0000    1.0000    0.0010    0.0003         0         0
>     8.0000    1.0000    0.0023    0.0008         0         0
>     9.0000    1.0000    0.0005    0.0002         0         0
>    10.0000    1.0000    0.0006    0.0002         0         0
>    11.0000    1.0000    0.0012    0.0004         0         0
>    12.0000    1.0000         0         0         0         0
>   Columns 7 through 12
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>     1.0000    1.0000         0    0.4150    1.0000    1.1000
>   Column 13
>     0.9400
>     0.9400
>     0.9400
>     0.9400
>     0.9400
>     0.9400
>     0.9400
>     0.9400
>     0.9400
>     0.9400
>     0.9400
>     0.9400
>
> Thank you very much for the help
>
> Yours sincerely,
> Nur
>
> On Wed, Oct 26, 2016 at 11:14 PM, Nazurah Nasir <nurnazu...@gmail.com>
> wrote:
>
>> Aren't I supposed to make the R and X in p.u. if I want to use them in
>> MATPOWER? Regardless, your simulation seems to be more sensible. But, I
>> just curious, so we don't necessarily change the R and X into p.u. values?
>>
>> Thanks for the response.
>>
>> On Wed, Oct 26, 2016 at 3:26 PM, Saranya A <asar...@gmail.com> wrote:
>>
>>> Hi Nur,
>>> Dont divide R and X with the voltage. I get the following power flow
>>> without those two lines.
>>>
>>> ------------
>>> runpf('LV10')
>>>
>>> MATPOWER Version 6.0b1, 01-Jun-2016 -- AC Power Flow (Newton)
>>>
>>> Newton's method power flow converged in 5 iterations.
>>>
>>> Converged in 0.02 seconds
>>> ============================================================
>>> ====================
>>> |     System Summary
>>>       |
>>> ============================================================
>>> ====================
>>>
>>> How many?                How much?              P (MW)            Q
>>> (MVAr)
>>> ---------------------    -------------------  -------------
>>>  -----------------
>>> Buses             12     Total Gen Capacity     261.0        -302.0 to
>>> 302.0
>>> Generators        11     On-line Capacity       250.0        -300.0 to
>>> 300.0
>>> Committed Gens     1     Generation (actual)      1.2               0.5
>>> Loads             10     Load                     1.0               0.3
>>>   Fixed           10       Fixed                  1.0               0.3
>>>   Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
>>> Shunts             0     Shunt (inj)             -0.0               0.0
>>> Branches          11     Losses (I^2 * Z)         0.23              0.16
>>> Transformers       0     Branch Charging (inj)     -                0.0
>>> Inter-ties         0     Total Inter-tie Flow     0.0               0.0
>>> Areas              1
>>>
>>>                           Minimum                      Maximum
>>>                  -------------------------  -----------------------------
>>> ---
>>> Voltage Magnitude   0.717 p.u. @ bus 11         1.000 p.u. @ bus 1
>>> Voltage Angle      -5.40 deg   @ bus 11         0.00 deg   @ bus 1
>>> P Losses (I^2*R)             -                  0.06 MW    @ line 1-2
>>> Q Losses (I^2*X)             -                  0.04 MVAr  @ line 1-2
>>>
>>> ============================================================
>>> ====================
>>> |     Bus Data
>>>       |
>>> ============================================================
>>> ====================
>>>  Bus      Voltage          Generation             Load
>>>   #   Mag(pu) Ang(deg)   P (MW)   Q (MVAr)   P (MW)   Q (MVAr)
>>> ----- ------- --------  --------  --------  --------  --------
>>>     1  1.000    0.000*     1.23      0.46       -         -
>>>     2  0.950   -0.744       -         -        0.10      0.03
>>>     3  0.905   -1.483       -         -        0.10      0.03
>>>     4  0.864   -2.206       -         -        0.10      0.03
>>>     5  0.828   -2.898       -         -        0.10      0.03
>>>     6  0.797   -3.541       -         -        0.10      0.03
>>>     7  0.770   -4.116       -         -        0.10      0.03
>>>     8  0.749   -4.607       -         -        0.10      0.03
>>>     9  0.733   -4.993       -         -        0.10      0.03
>>>    10  0.722   -5.260       -         -        0.10      0.03
>>>    11  0.717   -5.397       -         -        0.10      0.03
>>>    12  1.000    0.000       -         -         -         -
>>>                         --------  --------  --------  --------
>>>                Total:      1.23      0.46      1.00      0.30
>>>
>>> ============================================================
>>> ====================
>>> |     Branch Data
>>>        |
>>> ============================================================
>>> ====================
>>> Brnch   From   To    From Bus Injection   To Bus Injection     Loss (I^2
>>> * Z)
>>>   #     Bus    Bus    P (MW)   Q (MVAr)   P (MW)   Q (MVAr)   P (MW)   Q
>>> (MVAr)
>>> -----  -----  -----  --------  --------  --------  --------  --------
>>>  --------
>>>    1      1      2      1.23      0.46     -1.17     -0.42     0.055
>>>  0.04
>>>    2      2      3      1.07      0.39     -1.03     -0.36     0.046
>>>  0.03
>>>    3      3      4      0.93      0.33     -0.89     -0.30     0.038
>>>  0.03
>>>    4      4      5      0.79      0.27     -0.76     -0.25     0.030
>>>  0.02
>>>    5      5      6      0.66      0.22     -0.64     -0.20     0.023
>>>  0.02
>>>    6      6      7      0.54      0.17     -0.52     -0.16     0.016
>>>  0.01
>>>    7      7      8      0.42      0.13     -0.41     -0.13     0.011
>>>  0.01
>>>    8      8      9      0.31      0.10     -0.30     -0.09     0.006
>>>  0.00
>>>    9      9     10      0.20      0.06     -0.20     -0.06     0.003
>>>  0.00
>>>   10     10     11      0.10      0.03     -0.10     -0.03     0.001
>>>  0.00
>>>   11      1     12      0.00      0.00      0.00      0.00     0.000
>>>  0.00
>>>                                                              --------
>>>  --------
>>>                                                     Total:     0.228
>>>  0.16
>>>
>>> On Tue, Oct 25, 2016 at 10:31 PM, Nazurah Nasir <nurnazu...@gmail.com>
>>> wrote:
>>>
>>>>
>>>>
>>>> Hi all MatPower community,
>>>>
>>>> I am trying to develop a simple LV network in radial network
>>>> distribution. However, my model did not converge or if I scale the R and X,
>>>> the results is too big (which means the R,X) scaling is wrong. I tried for
>>>> one month now but still could get around why it is not converging.
>>>>
>>>> I need to work on this PowerFlow to work inside my bilevel programming
>>>> loop. but it seems my code won't work because the power flow is not
>>>> converging.
>>>>
>>>> I need help on verifying my parameter. Attached is my code that I
>>>> build. As the MatPower is in three phase balanced, I lumped my loads that
>>>> connected to a bus as one load, hence the voltage at the bus is 0.415kV. My
>>>> input power are all in kW, hence I change the impedance values accordingly
>>>> by multiplying it by 1000. The input power is just a dummy value of 0.1MW
>>>> because it will update itself in a loop. But since input power is in kW, I
>>>> should divide that by 1000 right?
>>>>
>>>> Thank you so much for the help.
>>>>
>>>>