Thank you so much for your help. It worked now after doing the
modifications that you suggested.

On Tue, Nov 8, 2016 at 1:51 PM, André Carvalho Silva <
[email protected]> wrote:

> Hi there Haneen,
>
> By thaking a quick look at your matpower case, it seems fairly obvious
> that the branch flow limits (rate A in MVA) are missing (they cannot
> be equal to zero).
>
> Also, you should put some P and Q limits in your generator (Qmin,
> Qmax, Pmin and Pmax generator fields).
>
>
> Best regards,
> André Silva
>
>
>
> Citando "Haneen Aburub ." <[email protected]>:
>
> > Dear Matpowers,
> >
> > I tried to run a simple AC OPF for IEEE 33-bus (12.66 kV) distribution
> > system using PDIPM solver, but it failed. It gave me the following error:
> >
> > IPM Numerically Failed: unable to solve Ax=b.
> >
> > My system has only a generator at bus 1 (ref bus) and a linear cost
> > function for that generator.
> >
> > The AC PF using NR converged fine, but I do not know why the AC OPF did
> not
> > converge?
> >
> > I tried to relax the voltage limits (0.9-1.1) and using the AC PF
> solution
> > as a start for AC OPF. But these options did not work too.
> >
> > Could you please help. I attached my case.m file
> >
> > Best regards,
> >
> > Haneen
> >
>
>
>
> ----------------------------------------------------------------