Dear Dr. Zimmerman,

Thank you so much for your corrections and notes. I agree with all of them,
and I do not think you are missing something.

Best regards,

Haneen Aburub

On Wed, Nov 9, 2016 at 2:17 PM, Ray Zimmerman <[email protected]> wrote:

> I assume this data is from the Baran, Wu paper [1]. A couple of comments
> ...
>
> 1. Setting RATE_A column to zero is actually correct for a case with no
> branch flow limits (see footnote 14 at the bottom of p. 49 in the latest 
> User’s
> Manual
> <http://www.pserc.cornell.edu/matpower/docs/MATPOWER-manual-6.0b2.pdf>).
>
> 2. In the case file you sent, all of the tie lines are in-service,
> operating as a meshed system, rather than the base radial configuration,
> and the branch impedance parameters for 5 of the branches (every other
> branch starting with the first) do not match exactly what’s shown in the
> paper.
>
> 3. I’ve attached attached a version of the case that I believe matches the
> data from the paper exactly.
>
> 4. Unless I’m missing something, the data given in the paper and the base
> case solution given in the paper are not consistent. For one thing, the
> voltages do not match, but even more glaring is the fact that the total
> load is 3715 kW, but they claim the total substation load is 5085.26 kW and
> that the losses are about 8%. Am I missing something?
>
>     Ray
>
>
> [1] M. E. Baran and F. F. Wu, "Network reconfiguration in distribution
> systems for loss reduction and load balancing," in IEEE Transactions on
> Power Delivery, vol. 4, no. 2, pp. 1401-1407, Apr 1989. doi:
> 10.1109/61.25627 URL: http://doi.org/10.1109/61.25627
>
>
>
>
> On Nov 8, 2016, at 3:07 PM, Haneen Aburub . <[email protected]> wrote:
>
> Thank you so much for your help. It worked now after doing the
> modifications that you suggested.
>
> On Tue, Nov 8, 2016 at 1:51 PM, André Carvalho Silva <
> [email protected]> wrote:
>
>> Hi there Haneen,
>>
>> By thaking a quick look at your matpower case, it seems fairly obvious
>> that the branch flow limits (rate A in MVA) are missing (they cannot
>> be equal to zero).
>>
>> Also, you should put some P and Q limits in your generator (Qmin,
>> Qmax, Pmin and Pmax generator fields).
>>
>>
>> Best regards,
>> André Silva
>>
>>
>>
>> Citando "Haneen Aburub ." <[email protected]>:
>>
>> > Dear Matpowers,
>> >
>> > I tried to run a simple AC OPF for IEEE 33-bus (12.66 kV) distribution
>> > system using PDIPM solver, but it failed. It gave me the following
>> error:
>> >
>> > IPM Numerically Failed: unable to solve Ax=b.
>> >
>> > My system has only a generator at bus 1 (ref bus) and a linear cost
>> > function for that generator.
>> >
>> > The AC PF using NR converged fine, but I do not know why the AC OPF did
>> not
>> > converge?
>> >
>> > I tried to relax the voltage limits (0.9-1.1) and using the AC PF
>> solution
>> > as a start for AC OPF. But these options did not work too.
>> >
>> > Could you please help. I attached my case.m file
>> >
>> > Best regards,
>> >
>> > Haneen
>> >
>>
>>
>>
>> ----------------------------------------------------------------
>> This message was sent using IMP, the Internet Messaging Program.
>>
>>
>>
>
>
>

Reply via email to