Did you try the steps outlined by Jose Marin in the last entry under FAQ #5?

One other suggestion regarding the use of runcpf() is that the key is to find a 
modified solved power flow to start from. You could try reducing the loads to 
10% of the original and running an OPF (possibly with unconstrained line) to 
get the base case for your CPF.

   Ray


> On Apr 25, 2017, at 4:30 AM, Liang, Chen <[email protected]> wrote:
> 
> Hi MatPower users:
> 
> I'm now using MatPower to simulate the power redistribution in a cascading 
> failure events. However, I met some convergence issue using AC power flow to 
> compute the power redistribution.
> 
> Here is what I did:
> -- Use 'case2383wp' as the dataset and set branch power constraints using N-1 
> security constraints.
> -- Randomly select 100 line tripped as the initial line failure.
> -- Extract islands and run AC power flow for each islands with at least one 
> generator.
> -- Find new line failures and redo step 3 until there is no new failure.
> 
> AC power flow succeed for the first round of computing the redistribution. 
> However, it turns not to converge for the second round for a large connected 
> network [see attached case_info]. On the other hand, if I change to run DC 
> power flow, the algorithm always gives good results.
> 
> In addition, I tried the suggestion on FAQ 5v. Most of time runcpf doesn't 
> converge either. Any suggestions on how to deal with the convergence issue 
> for AC power flow?
> 
> Regards,
> Chen
> 
> 
> 
> 
> case_info(mpc)
> 
> Checking connectivity ... single fully connected network
> Elapsed time is 0.106501 seconds.
> ================================================================================
>                         Full    
>                        System   
> Number of:           ---------- 
>   buses                  2060   
>   loads                  1599   
>     on                   1599   
>     off                     -   
>     fixed                1599   
>     dispatchable            -   
>       on                    -   
>       off                   -   
>   generators              290   
>     on                    290   
>     off                     -   
>   shunt elements            -   
>   branches               2489   
>     on                   2412   
>     off                    77   
>     ties (off)              -   
> 
> Load                
>   active (MW)       
>     dispatched          21508.1 
>       fixed             21508.1 
>       dispatchable          -   
>     nominal             21508.1 
>       on                21508.1 
>       off                   -   
>       fixed             21508.1 
>       dispatchable          -   
>         on                  -   
>         off                 -   
>   reactive (MVAr)   
>     dispatched           7176.0 
>       fixed              7176.0 
>       dispatchable          -   
>     nominal              7176.0 
>       on                 7176.0 
>       off                   -   
>       fixed              7176.0 
>       dispatchable          -   
>         on                  -   
>         off                 -   
> 
> Generation          
>   active (MW)       
>     dispatched          21941.4 
>     max capacity        26111.4 
>       on                26111.4 
>       off                   -   
>     min capacity         9146.5 
>       on                 9146.5 
>       off                   -   
>   reactive (MVAr)   
>     dispatched           6286.3 
>     max capacity       416899.0 
>       on               416899.0 
>       off                   -   
>     min capacity      -403083.0 
>       on              -403083.0 
>       off                   -   
> 
> Shunt Injections    
>     active (MW)             -   
>     reactive (MVAr)         -   
> 
> Branch Losses       
>     active (MW)             -   
>     reactive (MVAr)         -   
> 
> DC line             
>   export (MW)       
>     dispatch                -   
>     max capacity            -   
>       on                    -   
>       off                   -   
>     min capacity            -   
>       on                    -   
>       off                   -   
> 
> Reference Buses     
>   num of ref buses          1   
>   ref bus numbers          18   