Hi MatPower users:

I'm now using MatPower to simulate the power redistribution in a cascading 
failure events. However, I met some convergence issue using AC power flow to 
compute the power redistribution.


Here is what I did:

-- Use 'case2383wp' as the dataset and set branch power constraints using N-1 
security constraints.

-- Randomly select 100 line tripped as the initial line failure.

-- Extract islands and run AC power flow for each islands with at least one 
generator.

-- Find new line failures and redo step 3 until there is no new failure.


AC power flow succeed for the first round of computing the redistribution. 
However, it turns not to converge for the second round for a large connected 
network [see attached case_info]. On the other hand, if I change to run DC 
power flow, the algorithm always gives good results.


In addition, I tried the suggestion on FAQ 5v. Most of time runcpf doesn't 
converge either. Any suggestions on how to deal with the convergence issue for 
AC power flow?


Regards,

Chen





case_info(mpc)


Checking connectivity ... single fully connected network
Elapsed time is 0.106501 seconds.
================================================================================
                        Full
                       System
Number of:           ----------
  buses                  2060
  loads                  1599
    on                   1599
    off                     -
    fixed                1599
    dispatchable            -
      on                    -
      off                   -
  generators              290
    on                    290
    off                     -
  shunt elements            -
  branches               2489
    on                   2412
    off                    77
    ties (off)              -

Load
  active (MW)
    dispatched          21508.1
      fixed             21508.1
      dispatchable          -
    nominal             21508.1
      on                21508.1
      off                   -
      fixed             21508.1
      dispatchable          -
        on                  -
        off                 -
  reactive (MVAr)
    dispatched           7176.0
      fixed              7176.0
      dispatchable          -
    nominal              7176.0
      on                 7176.0
      off                   -
      fixed              7176.0
      dispatchable          -
        on                  -
        off                 -

Generation
  active (MW)
    dispatched          21941.4
    max capacity        26111.4
      on                26111.4
      off                   -
    min capacity         9146.5
      on                 9146.5
      off                   -
  reactive (MVAr)
    dispatched           6286.3
    max capacity       416899.0
      on               416899.0
      off                   -
    min capacity      -403083.0
      on              -403083.0
      off                   -

Shunt Injections
    active (MW)             -
    reactive (MVAr)         -

Branch Losses
    active (MW)             -
    reactive (MVAr)         -

DC line
  export (MW)
    dispatch                -
    max capacity            -
      on                    -
      off                   -
    min capacity            -
      on                    -
      off                   -

Reference Buses
  num of ref buses          1
  ref bus numbers          18


Reply via email to