Thank you so much for your information Mirish that makes sense.
On 16 Feb 2018, at 23:09, Mirish Thakur 
<[email protected]<mailto:[email protected]>> wrote:

Hello,

You can set the renewable source as an active power generation source in 
generator matrix use PG column to set its maximum power output as Pmax and if 
it can not generate reactive power then treat that bus as PQ bus by numbering 
it '2' in bus matrix or in other way you can use it (same generation capacity 
of renewable) as a negative load in bus matrix.

regards
Mirish

On Fri, Feb 16, 2018 at 11:25 PM, Charalambos Ioannou 
<[email protected]<mailto:[email protected]>> wrote:
Sorry Sir, i didn't  understand what do you mean by that "set the bus to PQ if 
it is not able to provide voltage support (reactive power)."

On 16 Feb 2018, at 22:17, Ray Zimmerman 
<[email protected]<mailto:[email protected]>> wrote:

Yes, you can put renewable generators in mpc.gen. For power flow, you need to 
set PG to the desired output, with a positive sign and set the bus to PQ if it 
is not able to provide voltage support (reactive power).

   Ray

On Feb 16, 2018, at 1:55 PM, Charalambos Ioannou 
<[email protected]<mailto:[email protected]>> wrote:

Dear friends,

I would like to know if it is possible to represent the renewable generators in 
mpc.gen section as generators??

Moreover i would like this only for Power Flow not in Optimal Power Flow.

If it is doable i need to set the Pmax as the capacity of the renewable 
generator as a negative sing or positive sign?? and Qmax zero because the 
renewable generators do not dispatch reactive power

Thanks in advance.

Kind Regards

Charalampos