Dear Sarmad,

Thank you very much!  The caveats pointed by you are really helpful. Thanks!

Kind regards,
Jin

2018-04-13 13:16 GMT+10:00 Sarmad Hanif <[email protected]>:

> Dear Jin,
>
> Yes, you are right.
>
>
>
> However according to my experience, you have to be careful regarding the
> calculation of Jacobian of voltage sensitivities which might be required to
> translate Lagrange multipliers to LMP components.
>
> Matpower can give these sensitivities (Jacobian) from the function
> makeJac().
>
> So if you calculate Jacobian like makeJac(mpc), then it will give you
> sensitivity at the base case.
>
> Hence to get the updated Jacobian (representing the operating conditions),
> you need to implement something like makeJac(results_pf), where results_pf
> = runpf(mpc).
>
> Another issue, which I believe was corrected by Ray, was that if you have
> generators in the grid they were taken by-default as PV while making the
> Jacobian. So you might need to get the updated version of MATPOWER.
>
> Maybe Ray could shed some more light on making sure the steps for
> correctly translating Lagrange multipliers to LMP components.
>
>
>
> Hope it helps.
>
> Best,
>
> Sarmad
>
> *From:* [email protected] [mailto:
> [email protected]] *On Behalf Of *Ma Jin
> *Sent:* Wednesday, 11 April, 2018 5:24 PM
> *To:* MATPOWER discussion forum
> *Subject:* Re: Question about shadow price of line flow constraints in AC
> OPF
>
>
>
> Dear Sarmad,
>
>
>
> Thanks! Matpower provides the values of all Kuhn-tucker multipliers and
> Lagrange multipliers. So it is really a powerful tool which makes
> decomposition of the price possible if one wants to.
>
>
>
> Kind regards,
>
> Jin
>
>
>
> 2018-04-11 17:12 GMT+10:00 Sarmad Hanif <[email protected]>:
>
> Hi Jin,
>
> I couldn’t understand the issue you reported. But according to my
> knowledge, MATPOWER gives you the final price at the node, it doesn’t
> calculate individual congestion, loss, energy components.
>
> Moreover, for ACOPF, MATPOWER gives you and active ($/MW) and reactive
> power ($/MVar) marginal prices at respective nodes.
>
> Hope it helps.
>
>
>
> *From:* [email protected] [mailto:
> [email protected]] *On Behalf Of *Ma Jin
> *Sent:* Wednesday, 11 April, 2018 8:04 AM
> *To:* [email protected]
> *Subject:* Question about shadow price of line flow constraints in AC OPF
>
>
>
> Dear all,
>
>
>
> I feel confused about the unit of the shadow price of the line flow
> constraints in AC based OPF. Since the square of the apparent power is used
> when building the line flow constraints, the shadow price should be with a
> unit of $/(MVA*MVA). When it is converted to the shadow price $/MVA,
> MatPower times the RateA of that line, but for me, it more makes sense if
> it is multiplied with the apparent power flowing through the line. What is
> the reason behind multiplying that RateA. Thanks!
>
>
>
> Kind regards,
>
> Jin
>
>
>

Reply via email to