Hi,
   The AC power flow (runpf) is converging for your system, while the AC 
optimal power flow (runopf) does not. The reason being the line ratings (rateA, 
B, C) are less than the load they are supplying to. For instance, the load on 
bus 2 is 2.8 MW, but there is a single line 1-2 supplying power to this load 
and its rating is 1.5 MW. As such, the optimal power flow, which tries to 
adhere to the line limits, fails to converge. I suggest setting the line limits 
more than the load supplied at their ‘to’ buses.

Shri



From: <bounce-123103003-73493...@list.cornell.edu> on behalf of Αμαλία 
Μαυρογιάννη <amalia...@gmail.com>
Reply-To: MATPOWER discussion forum <matpowe...@list.cornell.edu>
Date: Wednesday, November 14, 2018 at 5:53 AM
To: "matpowe...@list.cornell.edu" <matpowe...@list.cornell.edu>
Subject: AC power flow not converge

I am working on an island system. I make a case where I depict the whole 
system. The lines are in 15KV and there are 3 generators in 5MW each. I run an 
AC power flow (runopf)and the message is Did not converge in 5 iterations. I 
have done the :

    define_constants;

    mpcbase = loadcase('casefile');

    mpcbase.bus(:, PD) = 0;

    mpcbase.bus(:, QD) = 0;

    mpcbase.gen(:, PG) = 0;

    mpctarget = loadcase('casefile');

    results = runcpf(mpcbase, mpctarget);

    results.cpf.max_lam


 and max_lam=10.5284.

The runcpf doesn't run at all.

The case is down.

Thanks