You are right that runpf() does not enforce voltage limits, but rather voltage 
set points of the generators. If you want to enforce voltage limits at all 
buses you will either have to use an OPF, or implement your own algorithm to 
control the generator voltage set points, switched shunt caps, transformer 
taps, etc.

    Ray



> On Oct 4, 2018, at 1:27 PM, Mohammadreza Chamanbaz 
> <[email protected]> wrote:
> 
> Dear All
> 
> I have designed generators active power and their voltage for an uncertain 
> network where there  is uncertainty associated with loads and renewable 
> generators. 
> 
> To test the feasibility of my design I need to run some Monte-Carlo 
> simulation and see if the control variables I have designed are robust 
> enough. For this reason, I use runpf command to obtain line flows and bus 
> voltages. It looks to me that matpower runpf command does not respect bus 
> voltage constraints (I might be wrong). Is there a way to enforce voltage 
> constraints in runpf command?
> 
> Regards,
> Mohammadreza