Maybe this can explain why a number of branches in case145 have negative
series resistance and impedance. I was wondering why this was the case.

Regards,
Elis

Den mån 3 sep. 2018 kl 08:29 skrev Jose Luis Marín <[email protected]>:

>
> I remember I did check extensively the conversion of two-winding
> transformers a few years back; however, I did not check 3-winding ones.
>
> You can check those formulas in this article by Siemens:
>
> "Modeling of Three-Winding Voltage Regulating Transformers for Positive
> Sequence Load Flow Analysis in PSS/E"
>
> https://w3.usa.siemens.com/datapool/us/SmartGrid/docs/pti/2010July/PDFS/Modeling%20of%20Three%20Winding%20Voltage%20Regulating%20Transformers.pdf
>
> --
> Jose L. Marin
> Grupo AIA
>
>
>
> 2018-08-31 0:12 GMT+02:00 Ray Zimmerman <[email protected]>:
>
>> This code was contributed by Yujia Zhu when he was at ASU working with
>> Dan Tylavsky. I’m afraid I’m not familiar with the details of that code,
>> but I’m pretty sure it was double-checked extensively against PSS/E’s
>> internal models.
>>
>>     Ray
>>
>>
>> On Aug 6, 2018, at 4:50 AM, Aebi Stefanie <[email protected]>
>> wrote:
>>
>> Dear all
>>
>>
>> I am trying to convert a PSSE .raw network case to mpc format.
>>
>>
>> I just discovered that I obtain negative branch parameters for some of
>> the 3-winding transformers in my System, i.e. x < 0, r < 0. I tried to
>> track the phenomenon and found the following section in psse_convert_xfmr.m:
>>
>>
>> R1 = (R12+R31-R23) ./ 2;
>> R2 = (R12+R23-R31) ./ 2;
>> R3 = (R31+R23-R12) ./ 2;
>> X1 = (X12+X31-X23) ./ 2;
>> X2 = (X12+X23-X31) ./ 2;
>> X3 = (X31+X23-X12) ./ 2;
>>
>>
>> I've got a number of branches where the negative term (e.g. R23 in
>> calculation of R1) is the biggest one, such that the resulting R or X is
>> negative.
>>
>>
>> Where does this definition come from?
>> And is there a way I can avoid getting negative line parameters?
>>
>>
>> Thanks for your help.
>>
>>
>> Kind regards,
>> Stefanie Aebi
>>
>>
>>
>