I remember I did check extensively the conversion of two-winding
transformers a few years back; however, I did not check 3-winding ones.

You can check those formulas in this article by Siemens:

"Modeling of Three-Winding Voltage Regulating Transformers for Positive
Sequence Load Flow Analysis in PSS/E"
https://w3.usa.siemens.com/datapool/us/SmartGrid/docs/pti/2010July/PDFS/Modeling%20of%20Three%20Winding%20Voltage%20Regulating%20Transformers.pdf

-- 
Jose L. Marin
Grupo AIA



2018-08-31 0:12 GMT+02:00 Ray Zimmerman <[email protected]>:

> This code was contributed by Yujia Zhu when he was at ASU working with Dan
> Tylavsky. I’m afraid I’m not familiar with the details of that code, but
> I’m pretty sure it was double-checked extensively against PSS/E’s internal
> models.
>
>     Ray
>
>
> On Aug 6, 2018, at 4:50 AM, Aebi Stefanie <[email protected]>
> wrote:
>
> Dear all
>
>
> I am trying to convert a PSSE .raw network case to mpc format.
>
>
> I just discovered that I obtain negative branch parameters for some of the
> 3-winding transformers in my System, i.e. x < 0, r < 0. I tried to track
> the phenomenon and found the following section in psse_convert_xfmr.m:
>
>
> R1 = (R12+R31-R23) ./ 2;
> R2 = (R12+R23-R31) ./ 2;
> R3 = (R31+R23-R12) ./ 2;
> X1 = (X12+X31-X23) ./ 2;
> X2 = (X12+X23-X31) ./ 2;
> X3 = (X31+X23-X12) ./ 2;
>
>
> I've got a number of branches where the negative term (e.g. R23 in
> calculation of R1) is the biggest one, such that the resulting R or X is
> negative.
>
>
> Where does this definition come from?
> And is there a way I can avoid getting negative line parameters?
>
>
> Thanks for your help.
>
>
> Kind regards,
> Stefanie Aebi
>
>
>