I don'w know about pump-like-turbines, but many have used the OutBack
Power MX60 charge controller with microhydro with success.
There are optimizations in the MX60 software especially for hydro too,
like letting it sweep from open circuit voltage all the way down to
battery voltage as well as disabling the mini-sweeping normally done
when used in PV mode.

The concern is when the turbine free-runs. The input (DC) free 
running turbine voltage must not go above 150 Volts Max when the 
hydro is unloaded, and the turbine (bearings) must be able to handle
the higher speed, which will happen from time to time. This may 
happen when batteries are full, battery side loads go away, or when 
the MX60 starts up or resets or is turned off.

  A diversion control on the battery side could be used as a failsafe 
or, better yet, a PV input side clipper can be built (non MX input 
shorting) to limit the MX60 input voltage and give the hydro a 
minimum load if necessary.  Nozzle and field adjustment may help as 
well.

Normally, a turbine optimized or wired for 48V battery using typical 
diversion regulation techniques will have quite a high free running 
open circuit voltage, (over 150 volts), so these installs are usually 
the ones that may have a problem with free running.

 If you check your unloaded voltage, use some capacitance across the 
output to reduce high voltage spikes. The short spikes will not be 
there when connected to an MX60 since the MX has a few thousand 
microfarads across its input, and will filter very well (after you 
are sure the average DC voltage won't skyrocket)

All this being said, I have heard of 28 percent or more increase in
hydro output from certain hydros, especially systems with long
wire runs.

boB ---  K7IQ
OutBack


--- In [email protected], tajuddin waris 
<[EMAIL PROTECTED]> wrote:
> Dear
> All member
>  
> As we know that MPPT (maksimum power point tracking) have been used 
in PV and wind turbine in order to improve efficiency the whole 
system. Is there any research  application of MPPT for microhydro 
particularly microhydro driving small turbine like pump as turbine ?
>  
> regard
>  
> waris
>  
>  
> 
> Send instant messages to your online friends 
http://uk.messenger.yahoo.com 
> 
> [Non-text portions of this message have been removed]






Does your company feature in the microhydro business directory at 
http://microhydropower.net/directory ? If not, please register free of charge 
and be exposed to the microhydro community world wide!

NOTE: The advertisements in this email are added by Yahoogroups who provides us 
with free email group services. The microhydro-group does not endorse products 
or support the advertisements in any way. 

More information on micro hydropower at http://microhydropower.net

To unsubscribe: send empty message to [EMAIL PROTECTED] 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/microhydro/

<*> To unsubscribe from this group, send an email to:
    [EMAIL PROTECTED]

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/
 


Reply via email to