On Mon, Oct 23, 2023 at 10:38:09AM -0400, Babak Pasdar wrote:
> I wanted to get some feedback as to what is considered standard A/B 
> power setup when data centers sell redundant power.?? It has always been 
> my understanding that A/B power means individually unique and preferably 
> alternate path connections to disparate UPS units.

Generally speaking, the definition of A/B has become muddied in recent decades. 
 It has almost become an inaccurate marketing term. 

Most sane people have the opinion (myself included) that when "A/B" power is 
offered, it is at minimum offererd as 2N UPS (different building entrance and 
MSBs and even physically separate UPS rooms are also desired on a true 2N A/B, 
but may not always be available).  Some data center operators go even further 
and architect load switching within their distribution, thereby preventing 
single-side/one-leg power outages for customers during most of their power 
maintenance activities

Some data center operators treat "A/B" as convenience for them to undertake 
maintenance and offload uptime responsibilities to their own customers, and 
require them to either undertake their own transfer switching and/or dual-cord 
every equipment, so that they can keep taking one side of the power system down 
for repeated maintenance.  This does not scale well for retail colo, as not 
every customer is going to be good at maintaining two PSUs for every single 
piece of equipment.

Some data centers also view "N+1" system deployment at the UPS as an acceptable 
form of A/B protection, as long as customer circuits are on different PDUs.

Long story short, whether you're receiving N+1 or 2N or 1N, it's important to 
inquire about how your power circuits will be architected and delivered by the 
data center, and either have that codified in the contract or reflected 
appropriately in SLA offering.  There is nothing wrong with the data center 
providing N+1 or 1N power, as long as they're transparent about it and that it 
is what you're willing to accept for the right terms.  However, simply 
accepting "we are providing you A/B power" or "we've never had primary power 
failure" are not sufficient to meet proper due diligence during a site 
selection process, unless you can accept the site outage occurring from time to 
time, or you're deploying your own power plant (i.e. DC power and batteries) to 
supplant data center's own power protection scheme.